The Wall
Forum / THE MAIN WALL / Buderus AM10
  • Post a Reply to this Thread
    Buderus AM10 (4 Posts)
  • Nick Nick @ 3:20 PM
    Contact this user
    Buderus AM10
    On the AM10 the second Menu item is the flow temperature setpoint. My question is what does it do, and what should i set it at? I am using the GB with rad panels, some radiant, and a hot watermaker.
  • Ray M Ray M @ 8:34 PM
    Contact this user
    AM-10
    The design temp should match the heat loss that the panel rads can handle. The other setting is the min temp that the the system can run at. RE: 14F odt 150F for system min temp 115F. The idhwh is not influenced by the AM-10 it is over ridden. Thanks Ray M Comfort Tech Corp
  • Joe@buderus Joe@buderus @ 8:20 AM
    Contact this user
    Thanks Ray, you are correct. Default display is outdoor temperature, push "Mode" button once and when there is a call for heat, the value displayed is what the target temperature is - default value "32", "Mode" button pushed again is the reference temperature at 14 degrees, push "mode" button - minimum temperature of the heating curve, push "Mode" button - warm weather shut down. The AM10 will not maintain temperature in the boiler or system if there is no call for heat. Please contact us if there are any questions.
  • Jamie Jamie @ 6:46 PM
    Contact this user