combined posts - pumping to/away piping math (6 Posts)
-
Draw more
Can you sketch out the rest of the manifolding ( supply and return)? How many feet to the highest pipe? vertical rise?
I have seen these things before. Piped in this way the pump at the boiler return was keeping a large header hot and keeping the flow through the boiler. I see some three way valves, if all the three way valves are stroked closed to the boiler supply then the boiler may not have the flow it needs.
good luck
-
Oh well
-
combined posts - pumping to/away pump math
here's the drawing of the piping and the numbers; is the exp tank to discharge side of pump piped correctly, and is the pump correctly sized?
-
N/A
January 26, 2008
@ 1:15 PM
What is
the circulator on the return being used for ? Is it running it's own zone ? I guess not if it's on 24/7 .
Are all the return pipes connected to this circ before it heads into the boiler ?
-
circs connected to boiler?
i believe so, and here are some pics but it's not easy to see it all
-
no, unfortunately,
i can't sketch it out because i don't have enough pics and i can't remember it all, but it's a 2 story bldg
-