Riello F5 Burner
-
Post a Reply to this Thread
Riello F5 Burner (12 Posts)
-
wat a minute
bob bona - i was just having a little fun... i just wanted to see what kinda of response from you people i would get with that kind of question... lol there's 4 possible suspects when the riello F series stays in pre-purged with immediate flame dropout... either bad, cad cell eye, control box, yoke, or valve stem... i just wanted to see how you guys would give an answers to that problem...lol sorry just having a little fun... -
oh by the way
that's a good try Marilyn you get 10 points lol -
oh wait !
should i just change parts, or maybe troubleshoot -
pre purge
Any chance the cell is seeing stray light and fooling the control into thinking there is an existing flame? -
riello
i did that... what else can it be... ? -
make sure electrodes are properly adjusted, too close and the burner will not light, but stay in pre-purge
-
riello burner
What could the problem be if the riello F5 burner constantly runs in pre-purge with immediate flame drop out??? -
Riello
Try Replacing Eye First...if That Does Not Correct problem,Try Replacing Control Box. -
Riello
Try Replacing Eye First...if That Does Not Correct problem,Try Replacing Control Box. -
wait a minute
I thought you said in the other thread that Riello rules, Becketts are N/G? Hmm. Check the tab clips where the xformer slides in. Make sure they aren't spread apart too far. Check Hg. To start. -
Riello
Just ran into this on a brand new install. Turned out to be just a nozzle. Start with the basics. -
The Riello Training guide says: Burner continues to purge and Lightoff with immediate flame dropout (530 SE Only) .Metal yoke coil missing .Coil wire #2 and #8 reversed .Low resistance of coid hoiding curcuit, terminals #1 and #2, (1350 ohms +/- 10%) Having no idea of that or what it means I pass on the information to you.