For an extreme case of oversizing and how it affected the system
go here: http://www.heatinghelp.com/newsletter.cfm?Id=119 To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional" -
2\" mains in an old gravity system
Should the EDR for the 2"Dia mains supplying to and returning from the radiators be added to the individual radiator EDR calculations in order to properly size a circulator pump? -
N/A June 28, 2008 @ 5:37 PM
zeke
Many guys thought you needed a larger circ to make the water go to the furthest rad, in reality it made the heated water short-cycle to the closest circuit on the pump.
As Dan said, usually overloading the circs motor and leaving the farthest circuits underheated.
Converted gravity systems only need the circ to provide a slight nudge.
Dave -
Quote"When servicing old hot-water heating systems that originally circulated by gravity, but now use circulating pumps, I began to notice a lot of oversized circulators. In some cases, the circulator was so severely oversized that the boiler could hardly get any heat out to the radiators. The water couldn't pick up much heat in the boiler or shed it in the radiators because it was moving so fast. There is very little resistance in the large pipes of a gravity system, so the" I am puzzled by this. Does it really mean that the boiler water is somehow short circuited? It defies my intuition but is of course wasteful of power. Could somebody explain this?