    I am installing twin 630k Fulton boilers 120# steam system. Running a 1.25" main  40'. What type and size trap should I use on the end of the main on the drip leg ?  Thank for any info ..

    Ed
    I have enough experience to know , that I dont know it all
  • Big Ed Big Ed @ 4:28 PM
    Contact this user

    No sure if posted correctly

    Two 630 Futons 120# steam boilers. Running 1.25" main 40' , what type and size trap should I use on the end of the main drip leg.?Thanks again
    I have enough experience to know , that I dont know it all
    This post was edited by an admin on September 29, 2009 4:29 PM.
  • kevinj kevinj @ 8:02 AM
    Contact this user

    Trap

    More info wioll be needed to size the trap. If you contact your Sarco or Armstrong rep they can size it. It will be about the smallest trap you can get.
  • joe lambert joe lambert @ 2:06 PM
    Contact this user

    Small is Correct

    I like using Float & Thermostatic traps these days, they are good at removing air that you will have on start-up.  You could use a 3/4" or 1" F&T-125 trap.  Make sure you get the orifice for 125 psi steam.

    I have seen some large traps on the main headers for boiler, these are there in case there is carry-over of boiler water into the steam line.  I don't usually recommend them but prefer to prevent carry-over at all costs.
  • kevinj kevinj @ 3:01 PM
    Contact this user

    Tiny boilers

    These must be real small to only need a 1.25" main.
  •  