The Wall
Forum / Radiant Heating / Pump SIze
  • Post a Reply to this Thread
    Pump SIze (4 Posts)
  • CamW CamW @ 2:12 PM
    Contact this user
    Pump SIze
    Can anyone tell me if there is an easy pump size formula for radiant circulation pumps. My floor has 300 foot loops of 1/2 diameter pex with 4 to a zone. Will a Taco 007 be big enough for this size loo.
    Thanks
    Cam
  • kcopp kcopp @ 6:37 PM
    Contact this user
    007 is a stretch
    a Taco 00R or a Grundfoss 15-58 would be a better fit.
    300' Feet of tubing is 18ft. of head.
  • NRT_Rob NRT_Rob @ 9:02 AM
    Contact this user
    where did you get that?
    18 feet of head? that's huge.
    you need to know your flow rate requirements to know what size pump you want. that requires a heat loss. or you can ballpark it. If you're zoning by pump though 4 loops is nothing. I would not normally recommend zoning by pump though unless you only have a couple of zones.
    NRT.Rob
  • Chris Chris @ 8:50 PM
    Contact this user
    Couple of questions
    Does that 300' count from the manifold and back to it or is there 300' in the floor and then leader lengths from and to the manifold? Are you running 100 percent water or is their anti-freeze in the system? Max loop length on 1/2" is 300' so you are way out on the curve. May have to use a TA009 or a Grunfos 26-99 depending on the anwser to the questions above. Keep in mind that we do not add up all the loops on the manifold. We only need to overcome loop that requires the highest head and flowrate. If we can overcome that we can overcome the others.
    "The bitter taste of a poor installation remains much longer than the sweet taste of the lowest price."