    Who has the best residential gas steam boiler (53 Posts)

  • Bobby3 Bobby3 @ 2:29 PM
    Contact this user

    Who has the best residential gas steam boiler

    My 30+ year old Peerless Steam boiler has sprung a leak,  temporarily being heald together with boiler Solder,   But I am in need of a a replacement. 
    i have used Burnham products in the past and have had good luck but am interested in what other options i should consider or just plain stay away from.
    Boiler is 1 pipe steam that was piped wrong when unit was system was converted from oil to gas many moons and many homeowners ago.  over the past 5 years that i have been in the house i have been able to make some improvements
    I have read the lost art of Steam heat and have picked up some helpful hints like relocating my main line vents.  Now i need some industry insight as too who makes the best boiler for my residential single pipe steam. I can vent to a chimney that needs to be lined or i can vent to the outside direct via power vent.
    Look forward to your thoughts Bobby
  • N/A @ 3:30 PM

    Gas Steam Boiler

    For efficiency, the consensus here among the pros as to the best gas boiler, is the Slant/Fin Intrepid or Smith G-8 with a power burner.  Let us know where you're located and possibly we can direct you to one of the guys that specializes in these units.
     For oil, the Burnham Megasteam seems to be at the top of the list and everyone is wondering when Burnham will set it up for gas.
    - Rod
  • Yep, what Rod said....

    I have used both on/off Heatwise burners and Power Flame modulating burners in  the Slant Fins.  If you are accustomed  to a quiet boiler, power burners do make noise like oil burners.  For a quieter option, The Slant Fin Galaxy boilers work nicely with a built in and very effective skimmer to help keep the boiler clean.  Also, somehow despite a smallish 2 1/2 inch tapping, they make bone dry steam up to at least 190,000 btu/hr input.   It is probably due to the large steam drum located off to the side of the main heat input to the castings and a cast in inclined plain near the steam outlet.  Slant Fin is the absolute tops for being the most principaled company that I have ever dealt with in any field. 

    The picture below is of a pair of Slantfins with Heatwise burners.
    The Steam Whisperer (Formerly Boilerpro)
    Chicago's Steam Heating Expert


    Noisy Radiators are a Cry for Help
    This post was edited by an admin on February 24, 2010 6:46 PM.
  • nicholas bonham-carter nicholas bonham-carter @ 6:55 PM
    Contact this user

    one more option

    you could always replace the sections if the boiler size is correct for the connected radiation load..and you have a stocking peerless distributor nearby.
    of course, the burner has to be in good shape too. the stem headers can be corrected at the time of replacement--nbc
  • jpf321 jpf321 @ 7:12 PM
    Contact this user

    S/F Interpid on Gas?

    I looked hard at the SlantFin Intrepid in my search for a new boiler .. their website states the Intrepid is OIL. I saw posts here from Steamhead that stated the Intrepid is "Gas Certified" but when I asked about where that info is available, I got no response. I did speak with the S/F regional sales rep and while he did admit that the Intrepids were rated for gas, he said I probably would have a hard time finding a contractor willing to put a gas burner in.

    On top of all of that, I have heard a rule of thumb is to not convert an boiler originally intended for OIL to GAS .. better to simply get a gas boiler in the first place ..

    so my question here is are Intrepids really in the field as GAS boilers and if so, what burners, specifically (Brand/Model) are going into them?

    thanks
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Steamhead Steamhead @ 10:54 PM
    Contact this user

    I thought I did respond, JPF

    but as busy as I've been it may have fallen thru the cracks.

    Slant/Fin's website has not been updated to reflect that the Intrepid boilers are approved for use with Carlin EZ-Gas, HeatWise SU or Midco EC power gas burners. You will need to call the company if you need documentation to this effect- I have it somewhere at the shop but it's probably buried. Ask for Bob Flanagan and tell him I sent you.

    We have several gas-fired Intrepids in service. Here are some pics of them. That's my partner Gordo in the third pic.
    "Reducing our country's energy consumption, one system at a time"

    Steam, Vapor & Hot-Water Heating Specialists

    Oil & Gas Burner Service

    Baltimore, MD (USA) and consulting anywhere.
  • jpf321 jpf321 @ 8:46 AM
    Contact this user

    thank you sir ...

    funny, when I was there for my impromptu visit, Cindy who is head of Marketing had no clue either. And Perry, the regional sales rep isn't in the loop either so it would seem. But thank you.

    i'm still on the fence i guess between sticking with oil or converting to NG .. once thing that i really am afraid of is sticking with oil and then springing a leak in my 50+y.o. underground tank in the front yard.

    as I understand it, in order to move to gas, I will likely need to
    1) line my chimney ($2000)
    2) call in a company to "abandon" my 550gal oil tank .. ($2500)
    3) additional NG piping (~$500)
    4) getting the NG company involved
    5) NYC code filings.

    sticking with oil avoids all of that. i also understand that moving to NG locks me into the monopoly of the NG company...

    can anyone weigh in on the need for chimney lining when moving from oil to gas?
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Luv'nsteam Luv'nsteam @ 5:10 PM
    Contact this user

    Chimney liner

    Jpf, while I cannot comment on the particulars of oil versus gas for a chimney liner, what I can tell you, is that it is about exhaust temperatures.  For instance, in my own application, the ancient boiler I took out had a flu temp of around 800 degrees.  My new Peerless WBV-3, has flu temps around 400 degrees.  The issue with the temp difference has to do with condition of your existing chimney.  If it is perfect and built correctly, you needn't worry about it (as far as I have learned: disclaimer- I am not a chimney or HVAC expert.  What I know, I learned from doing research for my own application).  The lower flu temps, when combined with moisture, create (sulfuric acid, I think) and if you have missing flu tiles and/or bad mortar joints, the acid can eat them away even further allowing exhaust gas into your home.  It is a safety issue.  If you are curious, I installed my own liner and I purchased a kit from Heartshearth.com.  It was easy to install and has lifetime warranty.  The flex liner I installed is made from titanium-stainless steel alloy.  I easily picked up the 35 foot long, 6" ID liner .  The other parts were made from 18-8 and 316 stainless.

    Mike
    This post was edited by an admin on February 25, 2010 5:12 PM.
  • jpf321 jpf321 @ 5:24 PM
    Contact this user

    thanks Mike

    can you provide a more direct link for Heartshearth.com .. since that one seems to come up as a parking/spam/ad site.

    jpf
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • N/A @ 5:58 PM

    Chimney Liners

    JPF - Try this link: [url=http://www.chimneylinerinc.com/]http://www.chimneylinerinc.com/ It has a lot of good info. Note  the comparison chart has the names of most of the chimney liner players. I  looked into liners last summer and ran across this site. Thumb rule for professionally installed is about $100 /ft.
    Go only with 316 TI  Edit: Thanks JPF for the correction. I will have to remember to check older links.
    - Rod
    This post was edited by an admin on February 26, 2010 3:01 PM.
  • jpf321 jpf321 @ 6:40 PM
    Contact this user

    thanks rod...

    that link didn't work .. but this link did : http://www.chimneylinerinc.com/
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Luv'nsteam Luv'nsteam @ 1:57 PM
    Contact this user

    functional link

    Hello jpf.  My apologies for the long delay.  Between no email alerts (I actually received one today for the first time in nearly two and half weeks) and working sun-up to sun-down, doesn't leave much time for squat. :  )

    Anyway, here is a good link.  I misspelled the first one.

    http://hartshearth.com/

    The site is a bit overwhelming and I think it could use some better organization, but hey, what do I know? lol

    As Rod said, it seems to run around $100.00 per foot to have the liner installed.  Be careful with your estimates though, most of the chimney people I did get estimates from where not installing anything anywhere near as complete as the kit I purchased.  If you do it yourself, let me know, as I learned a few things that will definitely save you time and effort.

    Mike
    This post was edited by an admin on March 9, 2010 2:04 PM.
  • Polycarp Polycarp @ 6:59 PM
    Contact this user

    insulation

    Did you insulate your liner?  or just go with the liner alone?  My reading suggests that insulation is most important with wood stoves and may not be necessary for gas appliances.
  • Luv'nsteam Luv'nsteam @ 7:44 PM
    Contact this user

    Insulated liner

    Polycarp, your findings are the same as mine.   Insulation is required by code (in my neck of the woods and perhaps many others also.  Maybe federal???) when using the liner with a wood stove (solid fuel).  Before I knew that, I did look into insulating my liner from hartshearth.  They have a really cool and easy to use (it appears.....) ceramic insulation and with an outer "Chinese finger-torcher-like" wire material that protects the insulation during installation.  It is not, however, inexpensive.  Hope this helps.

    Thank you,

    Mike
  • jpf321 jpf321 @ 5:07 PM
    Contact this user

    just spoke with BF @ Slantfin

    I just spoke with Bob F. and he confirmed as above .. it hasn't hit the website or brochures yet. You would order the boiler less burner and add a burner from the above options. Thanks Steamhead!
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Bobby3 Bobby3 @ 7:50 PM
    Contact this user

    Old G 461 Peerles compared to new Smith or slantfin

    so my 6 burner peerless with standing pilot rear draft hood compares to these recommendations how, the Smith and Slantfin appear to be oil boilers with a gas burner, how much louder are they? as i am sure my wife will wonder what the comotion is in the basement if it is too loud,  the other Slantfin with the skimming ports seems like a good alternative, is this most like what i have now????  Presently I am a genius to my wife for silencing the steam beast in the basement by moving some main line vents and dropping the pressure (thank Dan)  don't want to loose these crudentials when picking out our new beast for the basement.
    Bobby
  • Steamhead Steamhead @ 10:57 PM
    Contact this user

    They sound

    just like oil burners. I don't find that objectionable.
    "Reducing our country's energy consumption, one system at a time"

    Steam, Vapor & Hot-Water Heating Specialists

    Oil & Gas Burner Service

    Baltimore, MD (USA) and consulting anywhere.
  • N/A @ 1:51 PM

    QT Alternates

    Hi JPF-
    After reading your comments I think you may have run into a phenomena that is quite common in a lot of equipment companies. The company sells a piece of equipment in a standard configuration which is satisfactory for most applications. Quite often there maybe alternate configurations that could be applied in certain circumstances but the knowledge on this is kept quiet as the average installer is likely to get himself into trouble trying to install the alternate configuration.
    Our company sold a specialized hydraulic pump that was in the above category. We kept the alternate configurations very secret and only gave out this info. to the people who we knew had the mechanical and engineering knowledge to apply the pump in an alternate mode. We had a case of where one our sales people found out about the alternate configuration and without approval, passed it along to a customer with the end result that after many phone calls and emails I had to fly out and fix the pump and do a lot of PR damage control to save a big account. The word then went out to the sales dept. that the pump as far as they were concerned was only offered in standard mode and if they even mentioned otherwise they would face physical dismemberment.

    I’m not saying that this is the policy in this case but as this is pretty common policy in a lot of companies I thought mentioning it might help throw some light on the situation. It makes sense.  Put yourself in the position of a typical boiler company. After what we have seen on this board of the gross installations done by“knuckleheads” who are supposedly heating pros, would you disclose the knowledge of a more complicated  alternate configuration to the “average” installer or much less  a home owner off the street? I doubt it, unless your were very confident they knew what they were doing.
    Just a thought.
    - Rod
  • jpf321 jpf321 @ 3:15 PM
    Contact this user

    thanks rod ..

    thanks rod .. i wasn't trying to blame anyone for having secret alternatives .. but it seems like the info just wasn't even passed along .. like they "didn't get the memo" .. I think that in recent months, more and more people are switching to Gas (generally) and fewer people are looking at S/F (generally, at least in this market) .. so if they have a Gas configuration and are looking for better market penetration, it would make sense to unveil it .. it may be that they are not cost competitive as a gas option, or they are trying to remain niche as an oil option .. or trying to push their Galaxy line as their gas option .. i don't know.

    I did try calling Bob F. today but he is on vaca..I will try him again next week. 
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Some other information on Intrepids....

    If you look into the  Caravan version of these boilers  (modular boiler setup) you will also find they come with a dual fuel burner.  RE: the complexity of installing a gas burner,  I am not trained at installing oil burners, but I believe the installation and proper tuning of a gas burner is much easier than that of an oil burner.
    There appears to be a significant efficiency gain by going to a power burner Intrepid over a Galaxy or any other boiler of that type.   All the back losses from the flame are eliminated and the flame is much more efficient.   It is interesting that in a couple recent installs when I replaced some standard atmospheric gas boilers (with open ribbon burners (albeit the boilers were grossly over sized) and no stack dampers) with Intrepids equipped with gas burners the boiler rooms that used to be roasting are now quite cool.  Just remember that when looking at AFUE efficiencies they assume all the standby heat loss and burner radiation losses to the boiler room is usable heat.  With the Intrepids, there is very little of that heat,so it goes into the system instead.  Steamhead believes there is about a 7% improvement in efficiency.  I suspect that is quite conservative from my experience.
    If you go to a modulating burner (now these do take some work to tune in) you have another significant seasonal efficiency gain if the system has a variable load such as TRV's, multiple zones, or can be run with outdoor reset of pressure.  I believe another 12% gain in seasonal efficiency seems reasonable, maybe greater, over an on/off boiler. 
    Overall, together, the gain could improve seasonal efficiency by about 20% over open burner boilers.  That's something to look closely at.
    I hope to be putting together an article on these ideas in the next few months.
    The Steam Whisperer (Formerly Boilerpro)
    Chicago's Steam Heating Expert


    Noisy Radiators are a Cry for Help
  • N/A @ 3:41 PM

    Tremendous Potential

    It absolutely amazes me that the boiler/burner manufacturers haven't yet come up with an easily adjustable 2 stage burner setup, in gas and in oil, for residential steam boilers. It would seem to me that the first manufacturer offering this would own the whole market and would have homeowners lining up at their door.  With fuel now costing thousands of dollars a season and increasing, a potentially possible10- 20 percent savings is mind blowing.
    Boiler Pro's comments and input are, as always, very interesting and thought provoking. I look forward to his future article. For those of you who are reading this and haven't read Boiler Pro's most recent article you can find it at the following link.
    - Rod
    http://www.heatinghelp.com/article/11/Hot-Tech-Tips/1551/Taking-Another-Look-at-Steam-Boiler-Sizing-Methods-by-Dave-Boilerpro-Bunnell
  • jpf321 jpf321 @ 4:05 PM
    Contact this user

    the enthusiam is good...

    the enthusiasm for such a "breakthrough" boiler is great .. but don't forget that very very few "customers" ever see an ad or do research for a boiler .. they call in the plumber that their friend referred to them and take the plumber at his word .. that this is the right solution .. it is the plumbers that get marketed to .. if the incentives or profit margin isn't right for the plumber .. the customer is out of luck .. many plumbers that i've spoke with say .. i usually recommend or put in X brand .. but i'll install whatever you want me to...

    of couple of guys came with a particular brand's flyer in hand .. would be nice if the plumber instead came with a binder of several options and knew the differences between them .. but at the end of the day .. all boilers are the same aren't they .. so why bother. i mean .. a tea kettle is a tea kettle .. just depends on what color and size you want. 
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Charlie from wmass Charlie from wmass @ 4:48 PM
    Contact this user

    With what I see each day

    It is hard enough to get a single stage boiler properly tuned and cared for. Manufacturers are selling to the bulk market. I see a handful of boilers installed close to right and fewer yet tuned and cared for. Until the level of skill is common in our trade the staged boilers will be kept on the commercial end where the skill level is maintained due often to the Darwin effect. Keep it simple unless you can control it from your end.
    Cost is what you spend , value is what you get.
    cell # 413-841-6726
  • Charlie from wmass Charlie from wmass @ 4:48 PM
    Contact this user

    double

    post
    Cost is what you spend , value is what you get.
    cell # 413-841-6726
    This post was edited by an admin on March 8, 2010 11:48 PM.
  • Teserakt Teserakt @ 1:38 PM
    Contact this user

    Reviving Post...

    It's been a couple-plus years since this thread was active, but I've found the information quite, well, informative, and am wondering whether there might be any updates to "who has the best residential gas steam boiler?"  I'm in the market for a gas, steam boiler, and there certainly seem to be many many manufacturers, but it's difficult to find comparative information. 

    My current unit has an input rating of 290,000 BTU/HR with a Steam rating of 725 sq. ft.

    Much appreciated!
  • prairiekats prairiekats @ 3:32 PM
    Contact this user

    I need help too! glad to see the thread revived :)

    We have a 11400 sq ft 101yr old house that we love to death. We also love the steam radiators. REALLY love them. But the over 50yr old boiler went kaput finally. We hope to use both our attic and our basement before long so that's an additional maybe 1500sq ft. What should we be looking for?
    Also, we really need to be able to install it ourselves. We have 2 sons-in-law ready to help who are both pretty capable - one being a rancher who maintains all his own equipment.
    And we are thoroughly and completely broke! ha ha
    I've seen some galaxy models that seem perfect and maybe affordable. But reading through this thread it sounds like there are more things we need to buy in order to finish the installation?
    Sorry, lots of questions but if someone can help . . . YAY
    Becky
  • prairiekats prairiekats @ 3:34 PM
    Contact this user

    OOPS - that's 1400sq ft NOT 11400 YIKES

    sorry bout that
  • BobC BobC @ 3:53 PM
    Contact this user

    Smith and carlin EZ gas

    For that size house look into the Smith G8 series with the carlin EZ gas burner, they work great together but be warned they sound like an oil burner with that gas gun. They are very efficient  and seem to have a good reputation.

    Bob
    Smith G8-3 with EZ Gas @76,700 BTU, Single pipe steam


    Vaporstat with a 12oz cut-out and 4oz cut-in


    3PSI gauge
    This post was edited by an admin on October 31, 2012 3:54 PM.
  • prairiekats prairiekats @ 4:19 PM
    Contact this user

    Thanks Bob :)

    I'll definitely look into that one.
  • prairiekats prairiekats @ 4:41 PM
    Contact this user

    so where do you get the G8-3 EZ gas?

    I've looked online - all I get are other forums pretty much
  • Enreynolds Enreynolds @ 4:52 PM
    Contact this user

    Depends where you are

    I don't think I saw where you are hailing from prairiekats, but here is a link to Smiths Sales Rep locator.
    http://www.smithboiler.com/html/salesreps.asp
  • Enreynolds Enreynolds @ 4:57 PM
    Contact this user

    Depends where you are

    I don't think I saw where you are hailing from prairiekats, but here is a link to Smiths Sales Rep locator.
    http://www.smithboiler.com/html/salesreps.asp
  • nicholas bonham-carter nicholas bonham-carter @ 6:39 PM
    Contact this user

    replacement boiler

    make sure that the boiler you choose is sized to the radiation edr, and not to the old boiler, or the building heat loss!!!!
    the manufacturer's piping diagram must be followed exactly, but a drop header will be easier for fitting the piping.--nbc
  • Teserakt Teserakt @ 9:07 AM
    Contact this user

    Radiation EDR

    nbc-  Are you referring to my reference to current input BTUs and steam square foot rating?  I assume you're leading me to measure the capacities of the radiators in the home rather than base my decisions on current boiler size.  I'm currently making calculations based on the info here:  http://www.colonialsupply.com/resources/radiator3.htm

    Sound right?
  • jumper jumper @ 7:15 PM
    Contact this user

    what happened to hydrotherm ?

    Back in the eighties I bought some.
    As I recall they were cheaper than HB Smith and somewhat lighter.
    And I think there were steel boilers even cheaper and lighter.
  • Steamhead Steamhead @ 9:04 PM
    Contact this user

    The current-model Hydrotherm residential wet-base steamer

    appears to be the same as a Smith 8 series. These run very well with Carlin EZ-Gas burners. In fairness, I haven't tried any other gas burners in these boilers.
    "Reducing our country's energy consumption, one system at a time"

    Steam, Vapor & Hot-Water Heating Specialists

    Oil & Gas Burner Service

    Baltimore, MD (USA) and consulting anywhere.
  • Maine Vent Maine Vent @ 7:23 PM
    Contact this user

    Another choice

    Weil Mclean SGO's with a Riello Gas burner. So far mine has proven great. Along with massive venting and good pipe insulation. Gas for me here in Southern Maine is way cheaper than oil.
  • Steamhead Steamhead @ 9:08 PM
    Contact this user

    They also run well with the EZ-Gas

    or, on the larger models, the 201Gas. David Sutton has installed a lot of Golds with Carlin gas burners, and we have one out there with a 201Gas.

    Another good choice is Slant/Fin's Intrepid series. They were approved with the Carlin as well as the Midco EC series gas burners. HeatWise too, but unfortunately that company is out of business. They built a great burner.
    "Reducing our country's energy consumption, one system at a time"

    Steam, Vapor & Hot-Water Heating Specialists

    Oil & Gas Burner Service

    Baltimore, MD (USA) and consulting anywhere.
  • Paul48 Paul48 @ 9:23 PM
    Contact this user

    Parent

    Don't Hydrotherm and Smith share the same parent company? There is, as always confusion over Smith Cast Iron and HB Smith. It is my understanding that they are 2 different companies.My series 8- 5 section weighs over 700 lbs(250-300lbs heavier than some competitors), and it makes installation more of a challenge.That extra weight translates into thermal mass, and it doesn't get any better. IMO
    This post was edited by an admin on October 31, 2012 9:32 PM.
  • Steamhead Steamhead @ 9:26 PM
    Contact this user

    They do

    Mestek is the holding company's name.

    The old H.B. Smith company came under Mestek at some point, and is now just known as Smith. I bet Henry Bates Smith is spinning in his grave......
    "Reducing our country's energy consumption, one system at a time"

    Steam, Vapor & Hot-Water Heating Specialists

    Oil & Gas Burner Service

    Baltimore, MD (USA) and consulting anywhere.
  • Teserakt Teserakt @ 9:26 PM
    Contact this user

    Great photos

    Maine Vent-  Great photos!  And  nicely done plumbing, too.  Thanks for all of that.
  • prairiekats prairiekats @ 5:41 PM
    Contact this user

    couldn't get back on the forum yesterday!

    Thanks for info :)
    I still don't know what I'm doing though ha ha.
    I keep hearing things about burners. They don't come separately I hope? Is it just that the boiler companies use different burners made by other companies?
    I did want you all to know I appreciated your responses and I'll be back when we're closer to actually buying, I hope real soon. Then you can help us figure out how to install . . . Is there a recommendation for easiest to install? The old boiler here doesn't have much attached to it, doesn't LOOK hard, except weight. BUT . . .
    (thx enreynolds)
    Becky
  • SWEI SWEI @ 6:25 PM
    Contact this user

    gas power burners

    Are not made by the boiler manufacturers, but by third parties (Carlin, Midco, Riello, etc.)

    I just looked into this about a month ago for a customer.  Smith used to ship the G8 / EZ-Gas combo but no longer provides it as a prepackaged SKU.  No warranty issues from either manufacturer with the combo, but they do need to be purchased separately by the installer.
  • prairiekats prairiekats @ 5:42 PM
    Contact this user

    ps to enreynolds

    we're in Kansas - closest location in the link you gave is Indiana :)
  • Enreynolds Enreynolds @ 7:31 PM
    Contact this user

    Prariekats

    Call the sales rep in Indiana and ask him/her to provide you with the nearest distributors to you.  I would bet there is one closer than Indiana.  Otherwise, the internet has made the world a smaller place, so the sales rep should be able to arrange to ship you a boiler.
    Eric
  • StatenIslandhomeowner StatenIslandhomeowner @ 2:26 PM
    Contact this user

    help choosing a gas boiler

    I stumbled on this thread at the right time, since someone just revived it. I own an old home (1920s) with a gas heat, steam radiators & a 30 yr. old boiler that finally died. Leak, plus shot pilot ignition that will cost $1100 to replace. Made it through last winter with leak but now I need to get a new boiler quickly. I'm not very knowledgable, having been an apartment dweller for years, but I don't want to just take the installer's advice, since the few I've had in seem to disagree and didn't bother counting or measuring radiators. Brands mentoined are WeilMclain, Peerless, Crown, and New Yorker (owned by Burnham). Currently have Slant/Fin galaxy. Looks like 175,000 btu input/140,000 btu output. I'm going to try to learn to calculate btu needs myself. Can't afford to spend more than neccessary - we need a new roof, too. Any help with choosing greatly appreciated.
    Also, seems like most new models have electric ignition but after power outages courtesy of Hurricane Sandy, I'm womdering if there are other options. It's gonna be cold tonight.
  • ChrisJ ChrisJ @ 3:25 PM
    Contact this user

    Boiler brands

      I prefer atmosphereic boilers as they are quieter and simplier.  Electronic ignition or pilot both need 24V AC to operate.

    That said,  in my opinion the brand of boiler you buy is moot as they are all about the same.  What is NOT the same is who installs it and this is extremley important.   Once you find a good steam expert allow him to choose the boiler of his choice as well as the associated equipment.
    Forget about the name on the boiler and whether it uses rubber or steel connnectors and concentrate on finding a good steam expert to install the boiler, or learn to do it your self as I did. 
    Weil-McLain EG-45 connected to 392sqft of radiation via two 2" risers into a 3" drop header and 2" equalizer. Using Rectorseal Steamaster water treatment to greatly reduce corrosion in the boiler.

    Steam system pictures updated 6/5/14.
    https://picasaweb.google.com/thetube0a3/Boiler?authkey=Gv1sRgCImUxIqv9436MQ#
  • Rod Rod @ 3:30 PM
    Contact this user

    Replacing Boiler

    Hi-   I hope you weren’t too badly affected by Sandy, As to boiler replacement,  it would help if we knew a little more about your present system.  What type of system is it? Where is the leak  that you mentioned located?  It would also help if you posted some pictures of your system. Take the pictures from farther back so they include the boiler and the connecting piping. That way we can trace out the piping and determine where / how  it is connected to the boiler. If we need to see more detail we can just zoom in.
        If you don’t have it already I’d recommend you get a book available in the Shop section of this website. It’s called “We Got Steam Heat!” and wiull be a great help to you, Here’s a link to it:

    http://www.heatinghelp.com/products/Steam-Heating-Books/25/61/We-Got-Steam-Heat-A-Homeowners-Guide-to-Peaceful-Coexistence

    The following links are to articles/videos that may be of help to you:
    Video on the Importance of Boiler Piping Configuration
    http://www.heatinghelp.com/article/107/Steam-Heating/118/Steam-boiler-near-boiler-piping

    Replacing a Boiler Article
    http://www.heatinghelp.com/article/236/For-Homeowners/1490/How-to-have-a-boiler-replaced-without-getting-steamed

    Steam Heating Primer
    http://www.heatinghelp.com/article/321/Steam-Heating-Basics/128/A-Steam-Heating-Primer

    Boiler Ratings Explained
    http://www.heatinghelp.com/article/364/Boilers/143/Boiler-Ratings-Explained

    You mentioned about calculating the BTUs of the Radiators. I’ve attached worksheet that will help you with this. It will give you the figures to calculate the EDR (Equivalent Direct Radiation) in Square feet, of each radiator. If you then want the BTUs you multiply the EDR by 240. (1 Square Foot of steam radiation  equals 240 BTUs) though usually you can just use the total EDR to figure out the size of boiler you need. Be sure to read up on “Pickup Factor”.and IBR boiler ratings, The pickup factor in the IBR ratings is already figured in so you can match the total EDR of your radiators to the boiler directly to the boiler’s IBR rated out put in square feet of steam (with out including a pickup factor)

    I’m sure this is a bit overwhelming at first but with the help of the above articles and the book, it should quickly fall in place for you. Don’t hesitate to ask any questions that you might have and we’ll do our best to answer them.
    - Rod
  • prairiekats prairiekats @ 5:45 PM
    Contact this user

    Thanks Eric and Rod

    am taking all your information and suggestions to heart!
    as soon as I get the funds together . . . .
  • StatenIslandhomeowner StatenIslandhomeowner @ 6:42 PM
    Contact this user

    thanks

    Thanks for all the advice. I'm going to digest it and move forward. I've been all over the internet and this is the most helpful site I've found.
    Re: Sandy. We were lucky and just lost power for 2 days. Sadly, lots of people worse off.
  • jumper jumper @ 8:17 PM
    Contact this user

    pancake hydrotherm

    My recollection is that hydrotherm was made with horizontal castings unlike HB Smith, Weil-McClain & SlantFin which were the other ones I commonly saw.

    I also agree with ChrisJ that atmospheric is simpler. CGA mandates that you can turn off gas burner with a wall switch. But it's possible to set up emergency battery for electric outage . Not so with powered burner.
  • vaporvac vaporvac @ 12:57 PM
    Contact this user

    No emergency battery for PowerBurner?

    Wow! That's a drag. Why can't the power burners use a battery back-up?

     We often get tornadoes, ice-storms etc, where we've been without

    power for as long as ten days! I didn't have a back-up the my old

    atmospheric, but I'd have liked to have that option on the power

    burner.

    I do like the quiet of the atmospheric, but for the minimal cost

    differential I just can't justify the added fuel usage.  In a large,

    older home every bit helps ...alot. I've never heard an oil burner, so

    it's hard to get a fix on how loud these power burners are in

    comparison. Mine seems loud enough already, but I suppose it's

    something one gets used to? Thanks for re-viving this post. Colleen
  • ChrisJ ChrisJ @ 1:05 PM
    Contact this user

    oil burner noise

    I was able to hear my oil burner up in my livingroom as it was in the basement directly below the livingroom.  I can't even tell when my WM EG-45 (atmospheric) is on unless I'm in the basement with it.

    My oil burner was also a newer style with an acoustic cover on it.

    Now being fair I would say the typical oil burner is no louder than the averaged forced hot air furnace.
    Weil-McLain EG-45 connected to 392sqft of radiation via two 2" risers into a 3" drop header and 2" equalizer. Using Rectorseal Steamaster water treatment to greatly reduce corrosion in the boiler.

    Steam system pictures updated 6/5/14.
    https://picasaweb.google.com/thetube0a3/Boiler?authkey=Gv1sRgCImUxIqv9436MQ#
    This post was edited by an admin on November 7, 2012 1:08 PM.
  •  