Forum /
THE MAIN WALL /
BTU of plain copper pipe
Post a Reply to this Thread
BTU of plain copper pipe (4 Posts)
Can anyone refer me to a chart with the amount of heat unfinned copper pipe radiates? -
Heat loss from copper tubing...
There is a nice graph in John Siegenthaler's book, Modern Hydronic Heating, 2ND Edition, page 242. Figure 8-44. This applies for cases where the length of the tubing (in feet) divided by the flow rate (gallons/minute) is less than 20 ft/gpm. There is a complicated formula for when it is greater than 20.
The graph has the temperature of the water - temperature of the air in degrees F = 0 at the left and 140F at the right. At the left end, the heat loss is zero. At the right is the heat loss at 140F difference. There is a separate curve for each size tubing.
For example, at that end,
Tube size Heat Loss
2" about 150 BTU/hr/ft
1.5" 118
1.25" 102
1" 85
3/4" 68
1/2" 52
The lines are nearly straight. -
Burnhams heating helper
page 48 http://www.burnham.com/PDF/htghelper.pdf -
N/A March 11, 2010 @ 7:22 PM
Well JD is helping,,,
anyway,, I was "crappy" to him before, and for that I`m sorry,,,, but I think we understand each-other now. ;-)
PS- He gave some pretty valuable stats, (until you found the Burnham site) :-).