  • nicholas bonham-carter nicholas bonham-carter @ 1:01 PM
    Contact this user
    tekmar 269 question
    the tekmar 269/279 has an indoor temperature sensor, as well as an outdoor temperature sensor. what would the effect of temporarily opening a window [for fresh air] in the area of the indoor sensor?
    if i do this with my visionpro thermostat [equipped with a remote sensor] , then the boiler will run because of the lower temperature in the remote sensor area; but maybe the effect would not be the same for the tekmar.
    unfortunately, tekmar have no tech support email address that i can find.--nbc
  • MarkS MarkS @ 5:02 PM
    Contact this user
    Based on the manuals...
    here's what I think would happen:
    If the measured outdoor temperature is higher than the tekmar's "Warm Weather Shutdown" setting, then nothing will happen.
    Otherwise, if the room temperature is below the room temperature target, the tekmar will:
    1. Fire the boiler until the "steam established" point is reached, as determined by either a condensate return temperature sensor or a minimum "on" time, then
    2. Use the outdoor sensor to calculate the "on" portion of the heating cycle and continue to fire the boiler for that amount of time, then shut off.
    Cheers,
    Mark
    Homeowner, Royersford PA | 1890 one-pipe steam system | 3 floors | 14 radiators |
    Utica SFE5175S boiler | Beckett AFG burner @ 1.50 gph | 0-30 inH2O low pressure gauge | Vaporstat |
    245 MBH | 633 sf EDR | 607 sf connected load | Operating pressure: 2 oz |
    Four main runs (insulated) totaling 135 ft in length | All Gorton vents on mains & rads |
  • burky1957 burky1957 @ 10:04 AM
    Contact this user
    tekmar 279
    Are you opening the window for temporary fresh air or is this an every day thing?
    If it's everyday, then you should move the indoor sensor. It's purpose is to provide indoor temperature readings to the control to cycle the boiler.
    Tekmar likes for their reps to be first contact with tech service. They do have an excellent tech service dept. You can call them by phone or send a message through their regular e-mail. It will get to the right people.
  • Randy Baerg Randy Baerg @ 5:19 PM
    Contact this user
    tekmar steam control and tech support email
    First off for tekmar tech support you can email : customerservice@tekmarcontrols.com or call 250-545-7749.
     As for the steam control / indoor sensor question: If the indoor sensor sees the room temperature fall below the controls 'Room' setting it will cause the heating curve to be shifted up. In most cases this will cause an increase in the % on-time calculation.
    As long as you are not in WWSD.
    The control will fire for a longer period in the heat cycle - phase2 . The greater the amount of error the more shift will occur. There is a limit on how much shift is allowed. Usually recommend a heat cycle length of about 60 minutes to give the reset a good opportunity to vary on times.