i have been having heat problems. the burn stops firing and the error light is not on. when i cycle through the control items the boiler temp is well below the setting and the boiler target is three dashes instead of the number. when i enter the setting menu the target is set. the only way to fix it is to cycle the power to the unit but the fix only seems to last a day or two. if anyone has an answer that would be super
-
power?
How are you powering the control? I once solved an erratic control by giving it its own source of power. MB
-
power?
How are you powering the control? I once solved an erratic control by giving it its own source of power. MB
-
Mix Target - - -
The mix target shows three dashes when there is no mix demand signal on terminals 1 & 2, or if the outdoor temperature exceeds the Warm Weather Shut Down (WWSD) setting.
-
tekmar 360
You need to contact your local tekmar rep or call tekmar @ 250-545-7749.
Be prepared to explain your wiring and settings. They are only as good as the information you give them.
-