Hi everyone,
I have a solo 110 boiler that is supplying hot water to a restaurant.
I was called out last night because of no hot water.
I found the water pressure safety switch was leaking water.
Fortunately I had a replacement with me and replaced the switch.
Upon restoring power to the boiler the display shows "U 1.25".
I removed the cover on the Honeywell MCBA control and found a blown fuse just below the transformer terminals on the control.
I dried off the terminals to the pressure switch and checked other wiring.
Other than the foam lining the boiler being wet, everything seemed OK.
I replaced the fuse and restored power only to blow replacement fuse.
I then replaced the control board and the same fuse on the replacement control also blew.
I then removed the wiring harness cable from the control, replaced the blown fuse, restored power, blew fuse.
I switched transformers, replaced fuse, blew another fuse.
I rechecked wiring, everything seems to be OK.
I went to Radio Shack to get more fuses, 4 amp 250 V ?, all Radio Shack had was slow blow fuses.
Restaurant owner unhappy, I am not sure what to do next.
Any help would be appreciated!
Thanks. -
N/A June 26, 2010 @ 10:50 AM
TT F3 fuses
If I understand you correctly that fuse is for the 24V side, did you check to see if there is a backfeed from another 24V source? Are you using the standard Smart tank aquastat?
BTW-That Is a 4 amp 250V slow-blow fuse from factory. -
Find the problem?
Just wondering if you found the problem? -
John try contacting
Guy Wollard from TT e-mail gwooljr@comcast.net . -
One word
Multimeter.
You've got a short to ground or neutral. Likely from being wet. Ohm it out.