  • JohnGL JohnGL @ 7:44 AM
    Contact this user

    Triagel Tube Solo Boiler Problem

    Hi everyone,
    I have a solo 110 boiler that is supplying hot water to a restaurant.
    I was called out last night because of no hot water.
    I found the water pressure safety switch was leaking water.
    Fortunately I had a replacement with me and replaced the switch.
    Upon restoring power to the boiler the display shows "U 1.25".
    I removed the cover on the Honeywell MCBA control and found a blown fuse just below the transformer terminals on the control.
    I dried off the terminals to the pressure switch and checked other wiring.
    Other than the foam lining the boiler being wet, everything seemed OK.
    I replaced the fuse and restored power only to blow replacement fuse.
    I then replaced the control board and the same fuse on the replacement control also blew.
    I then removed the wiring harness cable from the control, replaced the blown fuse, restored power, blew fuse.
    I switched transformers, replaced fuse, blew another fuse.
    I rechecked wiring, everything seems to be OK.
    I went to Radio Shack to get more fuses, 4 amp 250 V ?, all Radio Shack had was slow blow fuses.
    Restaurant owner unhappy, I am not sure what to do next.
     Any help would be appreciated!
    Thanks.
  • N/A @ 10:50 AM

    TT F3 fuses

    If I understand you correctly that fuse is for the 24V side, did you check to see if there is a backfeed from another 24V source? Are you using the standard Smart tank aquastat?
    BTW-That Is a 4 amp 250V slow-blow fuse from factory.
  • Slimpickins Slimpickins @ 1:54 PM
    Contact this user

    Find the problem?

    Just wondering if you found the problem?
  • Tim McElwain Tim McElwain @ 8:35 PM
    Contact this user

    John try contacting

    Guy Wollard from TT e-mail gwooljr@comcast.net .
  • Tony Tony @ 9:23 PM
    Contact this user

    One word

    Multimeter.

    You've got a short to ground or neutral. Likely from being wet. Ohm it out.
  •  