The Wall
Forum / Gas Heating / Lochinvar Knight XL - KNB600
  • Post a Reply to this Thread
    Lochinvar Knight XL - KNB600 (10 Posts)
  • JStar JStar @ 8:25 PM
    Contact this user
    Two identical boilers in the mechanical room. Both are for heat. Only one does the DHW. Ongoing issues with the DHW boiler. I'll call this the bad unit. I get there today to find an ignition lock-out. Goes through pre-purge. Switches make. Igniter is sparking. Good ground. 24 volts to gas valve, hear the valve click. 2 seconds later, it drops out. No flame at all. Manometer on outlet of valve never moves from zero after the gas valve opens. Heat exchanger is clean. Intake/exhaust are clean and free of blockage (the previous month had us cleaning rocks and a McDonald's bag out of the exhaust). I even completely disconnected the intake/exhaust from the boiler. You can smell gas when the blower starts, but no flame. I switch the gas valve, and the control board from the working boiler. Same problem. And the good boiler still works. Then I switch the igniter and flame sensor between boilers. Start the bad unit up, and it fires without a hiccup. Unit cycles. DHW is back on for now until we can troubleshoot the bad parts some more. I go to the previously working boiler with the now "bad parts" expecting to see an ignition lock-out due to all of the faulty parts I just swapped into it. Jump it out to call for heat. Fires up. Cycles. Forehead smacked. Questions unanswered. Confusion setting in.
    What am I missing?
  • Charlie from wmass Charlie from wmass @ 10:56 PM
    Contact this user
    bad wire connection
    or the flame sensor was not grounding well. Get a spare flame sensor and have it on hand, then it will run fine.
  • JStar JStar @ 5:45 AM
    Contact this user
    Maybe.
    I have my reserve about the flame sensor only because I never actually got a flame on start-up.
    I went back the next day to the other boiler room with three boilers. Same exact problem. Switched the igniter and sensor. Now only the one boiler works. I think I've narrowed it down to a spark gap issue. The igniter that is currently working has a slightly larger gap than the bad one. The ignition lock-out time is 0.8 seconds. Maybe the smaller spark just wasn't able to light the fuel mix. We have a Lochinvar rep. going there with new igniters soon. I'll find out then. Although, I had a Lochinvar service rep. with me the first day, and he didn't have an answer either.
  • Tim McElwain Tim McElwain @ 2:57 PM
    Contact this user
    Typical gap
    should be about 1/8". This is a commercial version of the Knight and has some extra controls, which are typically a low and high pressure gas pressure switch. I would monitor the inlet and outlet gas pressure when attempting to fire. In going through the Sequence of Operation (Pages 11 and 12) of the service manual. The units 501 model and up will lockout if the second attempt fails. Does it try to do a second attempt? The flame on these units must be detected within 1 second after the sparking ends, next question does the sparking end or does it keep sparking - no flame and then lockout?
    I would also check to make sure all the parameters are set correctly according to the manual.
  • JStar JStar @ 5:54 AM
    Contact this user
    Operation.
    The gap looked to be about 1/8" just by eye. It does lock out after two tries. The sight glass into the heat chamber is so small that I couldn't see when or if the igniter was ever sparking inside. Can you meter the ground leg on the igniter to know when it's sparking without actually seeing it? I could barely hear it over the blower noise. I checked outlet gas pressure. It starts in a negative when the blower comes on, then goes to 0 when the valve opens. When I hooked up to the inlet side, I was reading 7", but as soon as the boiler started up, I got a pressure switch fault, so I couldn't read the inlet pressure while the boiler was running. I probably have a tiny leak in my manometer hose causing the pressure switch to trip.
    As for the parameters...do you think the blower is running as the wrong speed? What range should I be looking for? And why do all of the other boilers work? They are all piped and vented as close to identical as possible.
  • Tim McElwain Tim McElwain @ 11:12 AM
    Contact this user
    Yes it is possible
    that the blower is not getting up to speed or it is set incorrectly. I am not sure if the blower speed can be changed on these units. Some systems do allow you to change blower speed.
    Are you getting any kind of fault code when this happens? Also check the troubleshooting in the service manual on Lochinvars site pages 33 to 45. One thing also to check is there a "Ramp Delay" set up on this unit. I would also check to see if this is set to a Building Management System which could be set incorrectly.
    As for the gas pressure issue I would recheck that as the pressure switch could be faulty or you may have a drop in gas pressure when this unit fires. Is this unit at the end of the gas line, if so it could be dropping below the settings for the pressure switch.
  • Charlie from wmass Charlie from wmass @ 12:33 AM
    Contact this user
    I have had animals from bugs to small
    mammals and birds in blowers. also had cracked or bent blowers interferring with blowers reaching speed. All fun things to trouble shoot. did you check the intake pipe for debris?
  • JStar JStar @ 5:31 AM
    Contact this user
    Intake and exhaust are free and clear. I even had them disconnected from the boiler for a few tries.
    As far as I know, all 5 boilers on site are set-up (parameters, fan speeds, etc) exactly the same way, and 3 of them have never had a problem.
    I'm getting an Ignition Failure lock-out fault code. I believe it is expressed as "No Flame Ign". I have 7" W.C. on my gas inlet. It's the first boiler on the gas line in the mechanical room. Gas pipe size is correct. Other than the times when I had my manometer on the inlet side, I've never gotten any other fault codes during ignition trial.
    A few guys have gone there before me. All they did was clean the flame sensor and walk away. They said it was running when they left, but who knows...
  • Charlie from wmass Charlie from wmass @ 10:46 AM
    Contact this user
    Flame sensor then
    you can clean some many times and others only once before replacing. There seems to be no rhyme or reason to which ones last and which do not. also I was told nothing harsher than a dollar bill to clean them with. If that does not clean them they need replaced.
  • JStar JStar @ 6:34 PM
    Contact this user
    Can"t be flame sensor.
    Never got a flame.