The Wall
Forum / Strictly Steam / EDR / BTU's steam / hot water
  • Post a Reply to this Thread
    EDR / BTU's steam / hot water (4 Posts)
  • Steve Steve @ 4:14 PM
    Contact this user
    When I measure up an existing radiator and calculate the EDR, I know you multiply by 240 to get the BTU's for steam. But for hot water I believe you multiply the EDR by 150 for 170 degree hot water - I seem to remember reading this in one of Dan's books - can anyone clarify?
  • Steamhead Steamhead @ 4:24 PM
    Contact this user
    That's right
    assuming you're working with a max boiler temp of 180° F.
  • Brad White Brad White @ 6:29 PM
    Contact this user
    Correct, and
    keep in mind that the reference temperature (the 170F) is the "average" water temperature. This is what Steamhead is saying, re: 180F supply water, but presumes a 20 degree drop.
    If you size for condensing boilers using 140F maximum supply (Say 130F average assuming 120F return), you get about 90 BTUH per EDR.
    "If you do not know the answer, say, "I do not know the answer", and you will be right!"
    -Ernie White, my Dad
  • Steve Steve @ 11:21 AM
    Contact this user
    thanks
    thanks guys