  • jpf321 jpf321 @ 1:42 AM
    Contact this user

    so long fitzy ... hello slantie

    Work in progress...non-annotated pictures. More later. http://is.gd/gqumT
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on October 29, 2010 1:43 AM.
  • Rod Rod @ 2:30 AM
    Contact this user

    Pictures

    Hi jpf-
    Thanks for sharing your pictures with us. It looks like the new installation is coming right along. I really like your "2 stage" header!!!   It will be interesting to hear your impressions/comparisons with the new boiler especially since you have data from the old boiler's operation.
    - Rod
  • Dave in QCA Dave in QCA @ 8:03 AM
    Contact this user

    Excellent Install!

    Congratulations on your new boiler!  Please keep us posted on the performance comparisons.  I wish that the Slantfin boiler was available in a bigger model for my applicaiton.
    Dave in Quad Cities, America
    Pennco 40M-1050SA Cast Iron Atmospheric Boiler. Input 1,050,000. Downfired to 600,000 BTU Lo-fire, 825,000 BTU Hi-fire input,
    System = Early Dunham 2-pipe Vapor/Vacuum (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2
    Current connected load EDR= 1,287 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 8 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
  • crash2009 crash2009 @ 8:42 AM
    Contact this user

    Lookin good!

    So thats what you been busy with.  Lookin good!
  • TomM TomM @ 3:43 PM
    Contact this user

    congratulation

    congratulations on your new baby!!
    -
    man, at 31" high, those Slantys really up your "A" dimension.  That's the perfect solution for a low basement ceiling application.  Mine's only 6 feet. 
    -
    one question:  Now whaddya gonna work on?  A new boiler sounds great and all, but the lack of constant tinkering, troubleshooting, and repair would probably bore me.  i guess you could always add a radiant loop or something.
    beautiful Conshohocken PA
  • jpf321 jpf321 @ 12:25 PM
    Contact this user

    updated/more pics and THANKS!!

    First I want to publicly THANK:

    + CHRIS - Simply #1
    + John, Mark, Jerry, Teddy - master steam fitters
    + Karen @ www.SimplyPlumbing.com - on the ball and fantastic to work with
    + SteamHead for his experience and work with off-wall emails
    + All the other WALLIES and of course DAN for making this site possible
    + My wife and Kids :-) -- for not sticking their noses in too far and not hugging me when I'm filthy.
    + "Uncle Al" - always there for me with knowledge, a tool or a story
    + John S., Bob, Larry @ SlantFin Tech Services & Perry in Sales & Bob F.
    + The guys at Blackman, AMAF, Solco Supply Houses
    + Mother Nature for great install day weather

    Updated, somewhat annotated pics:
    http://picasaweb.google.com/jpf321/BoilerInstall?authkey=Gv1sRgCPLo55SeuNyGfQ#

    The first firing took 2hrs to go from room temperature to 6oz.

    Still quite a bit to do yet. Will keep informed.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on October 30, 2010 12:35 PM.
  • Mark N Mark N @ 7:41 PM
    Contact this user

    New Boiler

    I'm glad to see you've had a new boiler installed. I do have a few questions. Why didn't you install a probe type lwco? Also looking through your install photos I see you used a Gifford loop instead of a Hartford loop. In your photo you have it labeled 1/2" above the NWL. According to Mr. Gifford's website the bottom of the close nipple used in the Gifford loop should be 1/2" above the waterline. The waterline is defined as the level at which the automatic water feeder would start feeding water. Did you just label the photo wrong? If the bottom of the loop is above the NWL won't it be hard to get the water back into the boiler?
  • jpf321 jpf321 @ 10:40 PM
    Contact this user

    LWCO and Gifford Loop

    Hey Mark .. thanks for the ?'s



    Funny you should ask about the LWCO as that was, I think, the first
    question I had when we unpacked the boiler .. the Intrepid TR-30-SU (SKD
    + bUrner)  is less LWCO, although I really thought it may have been
    part of the shipment since they provide a P-trol, I thought the lack of a
    LWCO was odd, but indeed, that's the configuration.



    So, to answer your question, I did this on a very tight budget. The 67 I have installed came off my Fitzy .. I took it apart, cleaned it thoroughly, changed the gaskets (2 gaskets $4ea from Statesupply.com), and happily put it back in service. I also happen to have scavaged a few other 67's from local boiler replacements in the neighborhood (I love when I see a boiler replacement going on somewhere and stopping to ask the guys for the parts and controls they will otherwise discard.) So I have spare parts for the 67. I am considering adding a probe as a secondary (with manual reset) however, it may be quite tight as the tapping is in the area of the skim port/current 67. There is much discussion on the WALL regarding the pros/cons of a 67 vs. a probe.
    + Contrary to popular belief a probe is not maintenance free and should be cleaned yearly.
    + As well, if there is any foaming, surging or priming, the probe may read a false LW and cause short cycling.
    + The 67 has a much more stable waterline I think.
    + I don't mind dropping in to visit my boiler every now and again and blowing down the 67 (as someone asked above, what will I have to tinker with now that I am all new?).
    + Lastly, I get a certain calming satisfaction out of dumping rusty water and seeing it run clear (I'm sure all the hardcore WALLIES would agree on this).



    The correct answer is both should be installed and one should be manual reset. I think one of the biggest reasons for boiler replacements is fire with no water, so it's better ($$$$) to be redundant in this area.

    Please note as well that I do NOT have an auto-feed, a decision that my installers couldn't wrap their heads around. A couple of reasons for this: 1) I'd like to have an understanding about how often my unit needs water since the need for water is very telling of other possible problems. 2) Everytime fresh water is added, it brings more dissolved Oxygen which is a steam systems & boiler's worst enemy. 3) This is a Catch-22: If I go on vacation, I don't want to risk an autofeed failing open (I have seen the results of this problem first hand and it is not pretty) HOWEVER, if I dropfire on LW, and I'm not around, my pipes/house might freeze. So this is a NET NET no-win situation, but somehow I feel more comfortable with the advantages of #1 and #2 than pessimistic about my house freezing.

    Regarding the Gifford .. again there was a bit of discussion about this with my installers, I actually had to print out Mr. Gifford's article and have them read it (keep in mind that the are native Polish, so even reading it was a bit of a struggle for them). Anyhow, NWL as I understand it is Normal Water Line, as defined in the I&O which is in this case 25-1/2" from the floor. If you read the direct quite from Gifford, you will see it says "Gifford Loop—a Hartford Loop with the bottom of the close-nipple at least 1/2 in. above the water level where the automatic feeder starts to add water." And in reality it could go higher. The purpose, put simply, is to decouple the boiler water level from the far end of the return stacking. Now, with regard to water having a hard time getting back, this is a non-issue provided you have adequate Dimension A. I don't have the LAOSH reference in front of me, but rest assured, I have (as noted above) plenty of Dim. A., additionally, my operating pressure if 6oz so I have PLENTY of Dim A. Simply stated, the stacking in the Dim A of my far return if more than adequate to return water to my boiler. I wouldn't have thought twice about going even higher than 1/2". The Hartford Loop is designed to keep the the water in the boiler as a safety precaution on a leaking return, however it has little benefit when it comes to system operation. The Gifford loop however, accomplishes both the safety aspect as well as is beneficial, as Henry points out in his article (http://is.gd/gvo4K), to the overall operation of the system.

    I hope that I've answered your questions, I'm happy to have feedback on the above by any who care to comment.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Mark N Mark N @ 9:17 AM
    Contact this user

    New Boiler

    I understand about tight budgets, I have one kid in college and another starting next fall. My new boiler came with a probe type lwco and a pressuretrol. I removed the auto-feeder. I think cycleguard makes a probe type lwco that deals with foaming. My problem with float type lwco is the weekly blow downs. Doing this causes a lot of water to be added. About once a month I need to add water. At that time I flush the mud leg and add water and then fire her up. I have a hartford loop on my boiler and haven't had any issues with it maybe on small systems the hartford is fine. The Giffford loop might be more practical on a large system.
  • jpf321 jpf321 @ 1:44 PM
    Contact this user

    another thing i just thought of

    with regard to decision to run manual feed. I want to control WHEN I add water to ensure that I'm not adding a large amount of cold water to a hot boiler.

    I think the VXT does deal with foaming better, but in a thread a while back, I also understood the VXT to shut the burner down every now and again to get a "good" reading. I didn't really enjoy the thought of having a shut down for my LWCO to determine the level. Even if the LWCO has a very short (few second) pause, my burner cycle is another 30secs to close shutter and then pre-purge, ignite, etc. If you have an auto-damper (which I don't) then you have to add another few seconds for it's activation .. all told, a VXT few second pause could run into a 1minute shutdown. Not to mention wear and tear on the parts and more chances of a mechanical process to fail (even though the LWCO is electronic).

    So, I figured the option for me was to reuse my trusted, spare parts available, MM#67 .. besides I have the original care and operation sheet for it stuck on a nail in my b-room from whenever it came originally.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Steamhead Steamhead @ 3:04 PM
    Contact this user

    Glad to help

    does it heat the house faster than the Fitz? 
    Steam, Vapor & Hot-Water Heating
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.

    Reducing our country's energy consumption, one system at a time.
  • jpf321 jpf321 @ 4:25 PM
    Contact this user

    tbd

    I'm performing ongoing skimming, flushing, cleaning. the last two days have also been occupied by kids halloween activities.I'm sure I'll be prolific on the subject ;-)

    thanks again.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Rod Rod @ 12:38 PM
    Contact this user

    Burner?

    I've been meaning to ask why did you decide on the Riello burner?  
    - Rod
  • jpf321 jpf321 @ 1:35 PM
    Contact this user

    ah yes, the great burner debate...

    you know that i try to do my homework and make fairly sound, reasoned, decisions .. i have to tell you that there is no easy way to decide (at least not being a professional and having the field experience dealing with dozens of burners) which to get.

    so i mixed a little of Charlie's "Cost is what you spend , value is what you get." philosophy as well as a survey of professionals that came in to quote the job (about 10 different outfits), my oil service company, comments on the internet and opinions of the WALLIES .. it still came down to pretty much a coin flip. Although most of the visiting professionals seemed to be keen on the idea of the Riello over a different brand. Perhaps it's also local preference, I asked them if there were parts readily available (YES), if they were easy to service (relatively), reliable (seemed to be) .. it ended up costing a bit more upfront (not too bad an increase) .. and I went with it.

    I don't intend to turn this thread into a burner debate, these were just my personal decision making paths when choosing a burner. If/When I ever switch to gas, I will have to re-educate myself all over again on burner options.

    Good question, no real good answer.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Rod Rod @ 2:03 PM
    Contact this user

    Riello Burner

    I was just curious as I know you research things out well.
    - Rod
  • jpf321 jpf321 @ 4:52 PM
    Contact this user

    Water Sample Pics

    I have uploaded a few pictures ( http://is.gd/gqumT) of my post-install water after running it a few times over the last few days .. I think the water is very cloudy because of a secret cleaning agent (which started out white in color) that was added last night.

    But regardless, you can really see how dirty the water is and the crud which has floated to the top.

    FYI my steam is of very poor quality right now and the boiler is surging like mad (I have overfilled it slightly since it was short cycling on LWCO, I have also had to turn my v-stat way up since the internal pressures are all over the place) .. basically it's doing what I would expect it to be doing at this time... cleaning and skimming is an important process and should not be disregarded.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Sil Sil @ 9:02 PM
    Contact this user

    The Water Pics Are Telling

    proof why skimming is so important... Sounds like this will take alot of skimming before you come up clear.
  • crash2009 crash2009 @ 5:34 PM
    Contact this user

    Witch's Brew for Halloween!

    Thats quite the batch you are cooking. Looks like honey.  Fitzy was crystal!  I'm still spittin out chunks of threads, and hunks of Teflon. 
  • Sil Sil @ 10:13 PM
    Contact this user

    Kimax

    Seems like I am headed towards replacing my 1 1/4" return. I think I would like to put in a length of Kimax in the return - like JP has.

    JP, Where can I get a length of the stuff. What kind of fitting do you use? Looking at the SCHOTT website, the KIMAX drainlines start a 1 1/2". If that a non starter or do they make a coupling that will work with a 1 1/4" black pipe?

    I see SCHOTTs US headquarters is in the county I live in...
  • jpf321 jpf321 @ 10:44 PM
    Contact this user

    I sent you emails

    Sil - I sent you 3 emails that detail my correspondence with Schott and their sales distributor on Long Island (Schott does NOT sell direct) and what I ended up buying. Please read them all carefully and have the Schott Kimax catalog in front of you since everything is all by numeric code.

    If anyone else is interested in learning more about the Kimax, please contact me privately offline.

    I do caution however, that if I had budgeted money to spend on a steam part, a vaporstat would be my first purchase (along with low pressure gauge).. the 5-foot length of Kimax pipe runs roughly equivalent in cost to a new vaporstat.

    Thanks
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Sil Sil @ 11:17 PM
    Contact this user

    thx JP

    Thanks for the info. The stuff ain't cheap, but as I mentioned in the email, if I am installing it myself, I don't mind spending some of the savings on something like this.

    I also plan to order a 0-3psi gauge as well.

    Dumb question about putting in a new pigtail (I know... brass). Do you have to put water into the pigtail/trap before installing it?

    Your new boiler looks great. I hope the new steamer doesn't make you lose interest in the "art of steam".
  • jpf321 jpf321 @ 11:27 PM
    Contact this user

    pigtails ...

    fill themselves with water very quickly, and with crud a less quickly, but both are guaranteed to end up in them without any extra help from you :-)

    and don't forget a vaporstat.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on October 31, 2010 11:27 PM.
  • TomM TomM @ 12:47 PM
    Contact this user

    knocked down?

    did you purchase that boiler knocked down?  thoughts on that?  seen some prices for knock-downs that look pretty cheap online compared to the local supply houses.  almost 50% cheaper.  thoughts?
    beautiful Conshohocken PA
  • jpf321 jpf321 @ 1:29 PM
    Contact this user

    knockdown vs. packaged

    first, you have to understand that I am local to simplyplumbing.com so I was able to save on the shipping (but paid NYC tax) ..

    it's really not at all easy to determine, unless you are a supply house with a price book, or you trust the guy at the boiler company phone center, what the real differences are between a KD or a Packaged. In fact upon pick-up I was surprised it was less LWCO. So in the case of SlantFin SKD (Steam KnockDown) you get an unjacketed but fully assembled (and properly torqued) section assembly, a p-trol (not manual reset), glass gauge, misc. fittings for both, and a pressure relief valve, 0-30gauge and the jacket.

    If you get an "SU" that's a Steam KD with a bUrner (burner is obviously not installed, but factory tweaked and tested for that model boiler). I had to order the tankless coil as a separate line item part and you have to supply your own Aquastat. I upgraded(?) to the Riello burner. MAKE SURE if you get a SlantFin Riello KD, that you get the correct burner wire harness, this was a hiccup since I was shipped with a Beckett harness and that didn't work, they made good within a few minutes with a quick trip over to their factory (Thanks John S!)

    I'm not actually sure how a Packaged unit arrives (other WALLIES here might). But I do know that it has a LWCO. I'm not sure if it is pre-trimmed. When I was on the SlantFin factory floor working out my wire harness last week, all the boilers I saw being assembled were coming off the line with their jackets at the very least, I even think that they had their burners bolted on if I recall correctly.

    I spent a good long time piecing everything together, and working with Karen regarding pricing and what's included, it was a struggle for both she and I. But the installed results are well worth it, the savings over a packaged, maybe not so much. I did save by reusing a LWCO, but that's probably about it. In the end, it may pay to get a packaged unit, it's probably about breakeven. I'm not sure what they do about the skim port piping if you opt for a packaged with a MM67 (which is an option, but probably not common request) as the I&O manual states to use 5" nipples to trim the LWCO .. that will NOT leave enough room to get a skim elbow in.

    I hope this helps. If you have any other questions, contact me directly.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on November 1, 2010 1:41 PM.
  • jpf321 jpf321 @ 12:39 AM
    Contact this user

    a wishlist of sorts ....

    ... (or what to watchout for if you ordered like I did)

    1) That the boiler company, perhaps specifically/soley S/F, was more public about the different configurations, options and included parts for each. The only codes they have for steam are: SKD, SU, PZT (packaged steam with tankless), PZ (packaged steam without tankless, but arranged), and another I forgot which is Packaged Steam with no option for tankless (or is that Burnham). if you want a Riello, there's no code. If you want a 67, there's no code. But these ARE offered as real options. Burnham, on the other hand, is very good about this, they have a letter code for every option, they are public about it and it's logical (mostly).

    2) That S/F would, since they sell the units as Riello optioned, include a damn wiring diagram anywhere in their I&O for a Riello setup. The problem with the Riello if that it does not have an on-board T-T connection for a thermostat (or aquastat) .. when I called Tech Services at S/F .. I was told that I needed an R8845 Switching Relay .. fine, I got one .. now what? I was fighting with 3 separate wiring diagrams (Intrepid, Riello, R8845) none of which was very clear or concise about how they all play nice together, at the end, I got it figured out, but not without a struggle and some help from Uncle Al (he's an uber-master electrician that used to be on the UL advisory committee and even he admitted that I had every right to be confused). All the wiring diagrams in the I&O assume a burner with an onboard T-T (or perhaps make the bigger assumption that T-T really means a Relay) They have a few pages devoted to setting up the Riello burner, so you'd think that somewhere in that space, they could include a couple wiring diagrams.

    3) That S/F would edit it's I&O for longer nipples required for the MM67 if there is any intention to have the customer perform a SKIM (for which they have an entire section in the I&O devoted) Problem is that you can't Skim a Tankless Steam setup if you install a MM67 as per their I&O. They have a gorgeous half-page diagram about installing the MM67 (they even have a wiring diagram devoted for the 67), but the install diagram calls for 5" nipples instead of ~9"-12" nipples required. (This may be different if you don't have a tankless since you could perhaps trim the MM67 left of the sight glass)

    4) That when they are building out the Riello burner, they remove the stupid circuit diagram card in the Primary where the numbers are 8, 7, 6, 5, 4, 3, 2, 1 (right to left) where in fact the terminals are stamped (and wired) 1, 2, 3, 4, 5, 6, 7, 8 (left to right) OR force Riello to correct their card, OR make a corrected card and swap out the Riello card.

    It's no wonder that people don't read the I&O manuals, in my case it was not at all helpful in 3 crucial areas (LWCO trimming and Riello wiring I&O diagram and Primary wiring diagram card), and makes one lose faith that the other things the I&O has to offer are any use either.

    I know, I know, most people don't get a knockdown, nor do most people actually skim (so why have a skim section in the I&O?), nor do most people take this project on that haven't already done this dozens/hundreds of times already. But isn't that the problem, people automatically know what to do, in this case they probably automatically know how to install an SU Riello 67 so they don't read (and probably never have read) the I&O (because it was written when they were still wearing diapers and the Intrepid was called a Liberty) which DOES contain actual important information .. things like don't use copper on a header, no bullheaded T's, don't reduce supply down to 2" just because that's the only threading machine you have, etc.

    Sometimes people have hit their own reboot button and forget everything they have in their RAM .. and perhaps that's why I'm always chiming in on these forums, I started wish fresh, virgin Steam knowledge RAM just 11 months ago!! (My first post was last November looking for someone to do an onsite survey/checkup/tuneup...and boy am I glad I didn't find anyone, they would have come, spent an 30mins with me and I would still be STEAM STUPID) I am now STEAM SMART (to an extent .. others may argue this point), and I haven't been taught the wrong way to do any of this stuff, and I'm always trying to understand the right way and WHY it's the right way.

    I say this all quite seriously, but at the same time I have much love for S/F .. afterall, I'm invested now and happily so. Boy that felt good.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on November 2, 2010 12:56 AM.
  • MarkS MarkS @ 7:00 AM
    Contact this user

    King valve question

    Nice looking install, JP.

    Once you get the skimming and wiring all sorted out, you can always direct your attention to control. My own summer project has been instrumenting my boiler with relatively inexpensive real-time I/O that plugs into the USB port on a PC. Ultimate goal - DIY outdoor reset control. More on that in a later thread.

    I have a question regarding your king valve. In pictures of other installs, the king valve is installed either vertically or diagonally. In your case, it looks like there wasn't a lot of choice as to the orientation of the valve due to the piping arrangement, but I was wondering if there were other considerations, and if you have any concerns about water pooling in or near the valve.

    Cheers,
    Mark
    Homeowner, Royersford PA | 1890 one-pipe steam system | 3 floors | 14 radiators |
    Utica SFE5175S boiler | Beckett AFG burner @ 1.50 gph | 0-30 inH2O low pressure gauge | Vaporstat |
    245 MBH | 633 sf EDR | 607 sf connected load | Operating pressure: 2 oz |
    Four main runs (insulated) totaling 135 ft in length | All Gorton vents on mains & rads |
  • jpf321 jpf321 @ 9:05 AM
    Contact this user

    good question ..

    that was the first installed piece ... i don't remember exactly what the internal chamber of that valve looks like .. i don't have an answer for you, however, i can say that everything is quiet and i don't have any banging.

    can any pros comment on the internals of a 3" gate and whether this is a possibility for pooling?

    FYI, I too have a new "data toy" that I am patiently waiting to install boiler side... stay tuned...
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on November 3, 2010 9:07 AM.
  • jpf321 jpf321 @ 3:01 PM
    Contact this user

    today's task...

    insulation .. header and under jacket ..

    i went with 2" thick for the header .. one in-progress picture posted. i got the fitting covers as well moving to that next.

    i also stuffed the voids that are under the jacket and under the boiler. the insulation is rated to 1000defF I believe. I made sure to install it while the unit was running quite a while. even up against the stove pipe, no ill effect.

    pic(s): http://is.gd/gqumT
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • jpf321 jpf321 @ 8:24 AM
    Contact this user

    header insulated...

    Updated pics .. http://is.gd/gqumT
    header is insulated with 2" ..
    jacket cover is back in place ..

    interestingly, by having filled the voids under the jacket, my stack temp rose 250degF .. which I have to work decreasing on now.

    no i need to attend to the wiring .. almost done
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Rod Rod @ 11:45 AM
    Contact this user

    Boiler Insulation

    Hi- I think your packing more insulation around the boiler is a great idea! I've always questioned why the boiler manufacturers are so skimpy on boiler insulation. There are directives on how thick the piping insulation should be, but nothing on insulating boilers. Apparently the "Deadmen" thought insulating the boiler was a good idea as they have left us the "Snowmen"!   Interesting that your stack temperature has gone up. I wonder what that's all about? Please let us know what you find. Great looking job!
    - Rod
  • jpf321 jpf321 @ 4:26 PM
    Contact this user

    and DHW heaters...

    are certainly insulated better than a boiler...i think I remember reading somewhere that there is a boiler (perhaps on the commercial side) that is insulated a full 4-inches...here it is keep in mind this is a Hot Water Boiler .. http://www.dedietrichboilers.com/DeDietrichWeb/Pages/PagesDefault.aspx?ProductPageID=2 (also keep in mind that I have a tankless coil on here for DHW, so I care about standing losses)

    I think the flue temp rose because the boiler was not losing heat to the room therefore, any heat that was left over after exchange to the water, had no where else to go but up and out the chimney and no longer out the sides and bottom of the boiler. There are still hot spots on the exterior of the jacket .. I may add some additional hard-board foil backed insulation on the exterior of the jacket. a good experiment i suppose would be to pull all the insulation and see where things go .. but i just finished being itchy.

    at this point, i have had to down-nozzle my burner and decrease the pressure a bit to reduce my flue temps. i'm pretty comfortable with my readings and flame at this point. (3.4% O2, 13.2% CO2, 474degF Stack, 400degF NET on a .75gph x 70deg "B" @ 125psi (effective firing rate of 0.85gph))
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on November 5, 2010 4:29 PM.
  • Rod Rod @ 5:19 PM
    Contact this user

    Cures for Itchiness

    I've done a lot of work with different types of fiberglass over the years and here are a couple of recommendations to cure itchiness.
    1. When taking a shower, start with cool water and lots of soap first. Warm water opens the pores of your skin and gives the fiberglass a better grip. After the intial cool water soaping and a cool rinse, you can then take a regular shower.
    2. If the "itches" persist - Use some masking tape and wrap it backward around the palm of your hand with the sticky side facing outwards. Pat the itchy areas and this will usually pickup any fiberglass remaining
    3. Be sure to wash the clothing that contacted fiberglass separately from any other washing.
        In most states it is grounds for divorce if you get fiberglass in your wife's lingerie

    - Rod
  • jpf321 jpf321 @ 5:23 PM
    Contact this user

    thanks ...

    i knew about #1 and the divorce thing .. i like #2

    i guess you really want me to pull my jacket insulation out for testing purposes huh? eh why not .. maybe next week though :-) .. 
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • crash2009 crash2009 @ 5:51 PM
    Contact this user

    Insulation

    is a great invention.  I will use 2" on the header and risers next time.  Elbows go on easy huh?  Valves,T's, and reducing elbows are a pain. Is your header 4" or 3".  Either way its huge with the insulation on.  Can you "feel" any heat through 2" ?
  • jpf321 jpf321 @ 7:28 PM
    Contact this user

    yep .. huge...

    i've heard bigger is better ..

    the elbows weren't very easy since they are so close to eachother and i have several of them.

    i embedded a temperature thermocouple inside one of the header horizontals (2nd level) ... it gets up to 211.5 (but I haven't checked the calibration on the newly arrived probe yet) (http://www.katsci.com/products/el-usb-2-lcd.aspx -- new source for probes, a bit cheaper than last year .. and i got one with the LCD readout.)

    i can feel that the insulation is warmer than the room .. but except where I skimped over the flange union, no discernable "heat" .. i'm going to see about borrowing my friend's IR camera and take some pictures (that might also be a good time to pull my jacket insulation too) .. maybe early next week... (i've started quite a list for myself for next week huh?)
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on November 5, 2010 7:29 PM.
  • crash2009 crash2009 @ 8:06 PM
    Contact this user

    I heard

    it was all over for you.  New boiler and nuthin to tinker with :)  I can relate to tight elbows, I did my returns, hartford and eq with 1"
    This post was edited by an admin on November 5, 2010 8:11 PM.
  • jpf321 jpf321 @ 5:13 PM
    Contact this user

    IR Pics posted

    I have posted a great many IR pics .. mostly of the boiler .. a few of the house exterior and some rads .. they are all in Chronological Order .. with "T" being time of begin fire. The boiler had been at rest about 4-5hrs prior to the first pictures.

    if there are questions about anything, please let me know .. please provide filename or link if you need help with any Identification.

    IR Pics: http://is.gd/gOG6J
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on November 7, 2010 5:16 PM.
  • Mark N Mark N @ 6:48 PM
    Contact this user

    Boiler Run Time

    On some of the pictures I saw something like T-97. Does that mean the boiler had been running for 97 minutes. Did you run it that long just to get the pictures. My house becomes to hot when the boiler run for 30 minutes and that is in really cold weather.

    Mark
  • crash2009 crash2009 @ 5:57 PM
    Contact this user

    IR Pics

    Awsome dude!
  • Mike Kusiak Mike Kusiak @ 6:18 PM
    Contact this user

    Boiler size vs.EDR?

    JP, I read in one of your postings that with the new boiler it takes two hours for your system to build pressure. I am curious as to the size and firing rate of the new boiler relative to the connected EDR. I remember that you posted extensive data regarding firing times until pressure cycling occurred with the old system.

    When you get a chance, it would be interesting to compare the graphs and data of the new and old systems.
    This post was edited by an admin on November 7, 2010 6:20 PM.
  • jpf321 jpf321 @ 7:03 PM
    Contact this user

    yeah...a little long

    I raise my thermostat-temp 1 degF in 70 min. with an indoor/outdoor delta T of about 30. no other data at this time. I'm firing at an effective rate of 0.85 gph. it's rated for 421 sq ft. I have about 400 installed. I have tankless coil so that may effect steam output.

    I did have the aqua stat cranked for the pictures. for the pictures the boiler started @ 13:25 and I shut it down @ 15:01 the file name for the pics has the time of exposure.

    my old fitzy was rated for 726 sq ft. and would start cycling on pressure about 40 minutes in and was firing at about 1.75 gph
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on November 7, 2010 9:59 PM.
  • jpf321 jpf321 @ 9:55 PM
    Contact this user

    nearly finished pics ...

    i have thrown up a few pics after my wiring install last night .. i'm sure there are cleaner ways to do all the wiring .. but this works for me. http://is.gd/gqumT
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • jpf321 jpf321 @ 11:03 PM
    Contact this user

    k-wool GOOD .. heat loss BAD ... updated IR pics!

    I spent the day re-insulating my steamer .. only this time I had access to K-Wool .. man is this stuff cool .. literally ..

    I had to strip the entire jacket (er... I mean COAT) off to do it right .. and that required some creative tin-snipping since it was not my intention to un-trim the boiler. but she went back together pretty well.

    basically K-wool comes in a 25ft roll of 1.5" thick by 4" wide .. you can see some if you scroll down here: http://is.gd/gVceq .. it's a ceramic based batting like fiberglass only denser and itchier (datasheet: http://is.gd/gVf6W) . I needed about 55ft (2 and a bit rolls) to fully insulate the little guy...there is very little waste ..you can always find a place to stick a remnant.

    oh .. and the stack temp went up another 50-60dF

    I've posted some pics of the insulation job .. http://is.gd/gqumT

    as well as some very cool IR pics .. and a couple of collages that show IR without K-Wool (and time of fire) and WITH K-wool and time of fire... http://is.gd/gOG6J

            

    enjoy!
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on November 10, 2010 11:23 PM.
  • jpf321 jpf321 @ 2:58 AM
    Contact this user

    finishing touches ....

    Well it's been a long time coming .. but today I put some finishing touches on my boiler.

    I finished out the p-trol and vaporstat control trees .. all brass .. the vaportstat tree has an isolation value in case I want to raise pressure above vaporstat levels. additionally, it has a valve which will allow me to break pigtail vacuum after the boiler cools.

    I made a funnel/flush port from the tapping for the pressure relief valve. This will allow me to add chemicals if desired, or to connect a hose and flush out the boiler from above if desired.

    i have a brass porous snubber on order, I would have liked to have had it today .. oh well.

    I installed a Swiss Made, 0.000gal accurate Oil Flow Meter which was salvaged from a friend's junk pile. It has a Qmin of 0.25gph. I've uploaded a video of it running for 2mins (http://is.gd/gZCyd) .. without watching, can anyone guess how much fuel I pull from my tank in 2mins?

    Oh and of course I uploaded pictures of the controls trees, funnel/flush setup and fuel meter. http://is.gd/gqumT

    Lastly, I downfired my burner to the bottom of it's scale .. my air shutter is between 0-1 .. I have what I consider great combustion and stack temp. (1.6%O2, 14.3%CO2, 398ppmCO, 8%X-Air, Gas Temp NET: 364 http://is.gd/gZzxh) ... I'm burning at almost 50% of the factory set-up firing, which I attribute almost entirely from the K-Wool insulation.

    If I had to do it all over again, I'd have gotten an Intrepid TR-40 (1-size-up) with a Riello 40/F3 (1-size-down) burner... there's always next year ;-)
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Mike Kusiak Mike Kusiak @ 7:54 AM
    Contact this user

    Combustion numbers

    You might post those numbers on the oil heating section of the forum and see what the oil guys think. To me, the CO reading is very high, and the O2 level is low. If you increased the air slightly, your CO readings would drop dramatically. At 8% excess air, you are really on the edge.

    http://www.testo.us/portal/embedded/Sites/USA/MainNavigation/ApplicationInformation/HVAC_Refrigeration/Refrigeration/CombustionGuide.pdf
    This post was edited by an admin on November 13, 2010 8:09 AM.
  • jpf321 jpf321 @ 3:52 PM
    Contact this user

    thanks mike ....

    i did notice smoke with last night's setup .. i have made a slight adjustment and eliminated the smoke .. 2.4%O2, 13.7%CO2, 117ppmCO, 12%X-Air, Gas Temp NET: 404
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Mark N Mark N @ 8:24 AM
    Contact this user

    Would like to know

    JP does adding all that extra insulation affect your warranty in any way? Also how long does it take to get steam to the main vents, last rad on the system? How long does it run when just maintaining temp? How do these numbers compare to your old boiler?

    Mark
  • jpf321 jpf321 @ 8:46 AM
    Contact this user

    I'm working on..

    the data aspects. empirically, I burn 0.62 gph rather than 1.8+ from old boiler. but I run longer. I'll try to look at some data later this morning. I have been collecting it. but I've also been tweaking and tuning. I'm also adding a few TRVs today since I seem to be undersized but not necessarily underfired. but I do have a warm rom our two that I can throttle back

    I don't know if adding insulation affects warranty. I'll visit john@SF sometime this week and ask.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Mark N Mark N @ 9:47 AM
    Contact this user

    Seems low

    I'm not sure but .62gph seems low to handle and EDR of 371sqft. plus hot water through your tankless coil. If someone takes a shower when your making steam the tankless may draw enough to inhibit the boilers ability to make steam. It is still somewhat mild now bbut in the middle of winter this could lead to some serious discomfort.

    Mark
  • jpf321 jpf321 @ 4:34 PM
    Contact this user

    thanks mark...

    for pushing me on the numbers .. after two soot brush/vacs, quite a bit of advice and a new smoke pull .. i have settled into the following figures. COppm: 5 CO2% 12.5 O2: 3.9 XS-Air: 22%  Gross Eff: 85.5% Temp NET: 355 Smoke=0 Nozz: 0.65x70b @ 175psi Head=0 Air=2 ...

    you were right, I was waaay off the other day.

    as soon as I cleaned the soot off from my blunder, my stack temp dropped quite a bit...showing the importance of a clean boiler for heat transfer.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Maine Doug Maine Doug @ 6:29 PM
    Contact this user

    This winter

    you are going to be warm and toasty but way bored when all you have to do is collect numbers for system performance stats. ;-}
  • jpf321 jpf321 @ 6:50 PM
    Contact this user

    i hope so...

    and count my saved dollars ?
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • Mike Kusiak Mike Kusiak @ 4:56 PM
    Contact this user

    Combustion numbers

    Those readings look much better. I wondered about your relatively high stack temp and had a feeling it might have sooted up from the previous settings. Glad to see you have is sorted out.
  • crash2009 crash2009 @ 12:16 PM
    Contact this user

    Bored or Boring

    I'd rather be bored than boring.  I have been watching the "so long fitzy...hello slantie" show since it began October 29, 2010.  There has always been something new to read about, or a new picture.  Admittedly, a lot of the conversation is over my head, but then again, less than a year ago, I didn't know what a rad vent was, let alone what to do with it.  JPF keep up the great work helping the rest of us understand how things work. 
  • jpf321 jpf321 @ 2:11 PM
    Contact this user

    thanks crash

    thanks for following along .. i've tried to get it all right .. as I found out today, my wiring is still a bit off .. nothing critical but my Riello Air Shutter doesn't close ..
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • jpf321 jpf321 @ 2:12 PM
    Contact this user

    Riello with TT onboard

    as it turns out, Riello has a primary controller which has an onboard
    24V TT (http://is.gd/h9Zph) .. for some reason, this is not how SlantFin
    sends out the Riello. If they had, things would be alot easier.I'm trying to find out if Riello would care to swap my primary for a TT one .. stay tuned. 
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • jpf321 jpf321 @ 11:31 PM
    Contact this user

    a few notes ...

    yesterday, i decided to go back to my original "factory" nozzle size and firing rate. 0.85x70degB @ 160psi (1.08gph effective). my NET stack is around 420degF vs. 360 at my lower firing rate (0.65x70degB @ 175 (0.82gph effective)) ... although honestly, i may go back to a happy medium of 0.75x70degB and close down the turbulator a bit...this firing rate is really quite loud .. i think that closing down the turbulator really quiets the fire. i want to aim for the same stack temp only with a bit less HEAD. i think I can do it.

    i'm happy to report that my steam seems much more full .. that is, I was able to raise my t-stat 1degF in just over 30mins.

    i realize now that my earlier worries about the sizing may have been unfounded possibly because.
     1) my water was quite dirty early on, and has now cleaned up substantially
     2) I sooted up my boiler pretty good at some point
     3) my new TRVs in the bedrooms, kitchen and mudroom may be doing their job and shedding load when the room is already at temp.

    i want to decrease my venting on some of my near-t-stat rads (LR couch, LR Desk and DiningRoom) I think they all have Gorton 6s right now, i'm going to try 5s. My t-stat satisfied before I get a good load of heat up to 3rd floor.

    my wiring is still awry .. my electronic air shutter (EAS) doesn't close .. i have to delve into the wiring again, or just leave it as is since i've heard of some problems with the Riello EAS. (boy I wish I had the Riello with TT onboard control box) .. but having the EAS closed would keep the boiler a bit warmer longer rather than having an open draft right through the combustion chamber. (another reason to close down the turbulator perhaps)

    I'm blowing in some more cellulose next week...today I swiss-cheesed my bedroom with holes through the plaster/lathe .. fun fun .. (true brick house, easier done from inside) the heatloss from the room that I did earlier in the month was significantly decreased .. in fact her room kept getting warmer and warmer with each heating cycle, in this sense, the TRV there is wonderful. my interior wall temps ranged from 73degF in her room to 63degF in the room just below her's (next on my list obviously)

    i ordered up a new lascar datalogger to replace the defective FAR RAD unit...then I am going to RMA the defective unit and they will either fix it or send me a new one .. they have been very helpful and responsive, and I really appreciate that.

    sorry, no new pics today .. just a few follow-up notes about the state of the system as I have been mostly hands off the last few days.
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
  • jpf321 jpf321 @ 12:30 AM
    Contact this user

    a few notes on current operating status...

    on these current cold NYC days (in the low-20's with winds) ..my S/F TR-30 (with coil) firing factory specs (1.08gph) with a couple of bedroom TRVs in place (most set at about 69degF Macon setting #5ish) as well as Foyer and Kitchen TRVs to shed load (if possible/appropriate) is heating the house just fine. TRV's are almost all vented with Gorton C regardless of rad size (my goal is to heat room with TRV and have TRV shutdown)

    pretty much I come up to 7oz pretty quickly after Main Vents Close (8mins from t-stat call) and then hover right there @ 7oz with no burner modulation for almost the entire cycle (i think my v-stat is set at around 7-9oz)... sometimes I see a momentary pressure drop mid-cycle, likely a TRV has just opened, or perhaps someone just ran some DHW .. this last cycle I only cycled on pressure once towards the very end.

    the t-stat is a constant 69degF (turned down recently from 70degF) with no setbacks and a 0.5deg swing.

    the system is quiet as a mouse .. no hissing from vents. sometimes (once every 5th cycle perhaps) i get a bang which i attribute to either 1) a TRV with faulty vacuum breaker (i know which one) opening up mid-cycle and releasing held rad water into horizontal runout or 2) gifford loop if I shutdown on pressure, depending on where in the system the bang is heard.

    losing about 1/8th inch of water every 4-5days. all returns are above ground no visible leaks in system. #67 LWCO blowdown requires quite a bit of water loss

    system water (glass pipe and sight gauge) is crystal clean except for some settled rust particles in glass pipe. I'm due for a skim (why not, it's on the frequently suggested solution list)

    i still haven't corrected my wiring to operate the Riello Electronic Air Shutter (currently always open) .. it's on the list. After my meeting with SlantFin, they posted online their latest and greatest I&O which contains the correct wiring diagram for Riello Steam Tankless #67.

    my combustion numbers are consistent. after installing my Itsa Oil Meter on 11/12/2010 I have burned as of current time 171.25gals of #2 oil .. HDD since 11/13/2010 = 652.7 so that works out to 0.26gal/HDD .. and that also means that heating season is about 1/7th over since our average HDD per season is about 4400 HDD here in NYC. FYI.. for those following along at home .. I am on track to consume almost exactly the same amount of fuel as last year..1100gals (although I don't have pre/post-main vent data..i installed main vents by this time last year) However, 1) I don't have to fear my boiler is going fail on the coldest night of the year and 2) I have learned a tremendous amount and 3) I have made new friends and 4) I have something to talk about at parties and 5) the home resale value has increased. The money spent is equivalent to a couple of college courses and I have enjoyed it more than college. Time get new windows :-)

    my cycle lengths are consistent but frequency of cycles change depending on HDD (greater HDD greater building Heat Loss based on delta-T)

    I haven't been breaking my v-stat pigtail/0-20oz gauge vacuum manually, and the 0-20 seems to find 0 eventually. lastly, my snubber is snubbing.

    i'll post some new data charts tomorrow. over here... http://www.heatinghelp.com/forum-thread/132987/let-the-data-begin
    Entire Site | MAIN WALL | Strictly Steam | Off-Wall

    1-pipe Homeowner - Queens, NYC
    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    venting worksheet download | Lost Art Of Steam Heating | my NEW system pics | my OLD system pics | old patents | pipe size chart | Copper Size Chart: K,L,M
    This post was edited by an admin on December 15, 2010 1:04 AM.
  • Dave in QCA Dave in QCA @ 2:14 PM
    Contact this user

    Replacement windows? Please say it ain't so!

    Before you run out and buy replacement windows, you need to do some research.  Actually, I can tell that you are the type of person who researches everything.  Replacment windows are not all they are cracked up to be, and often never provide a reasonable payback.  There are other options that are better.  See this link,  http://renovatedsm.com/book/export/html/376
    Dave in Quad Cities, America
    Pennco 40M-1050SA Cast Iron Atmospheric Boiler. Input 1,050,000. Downfired to 600,000 BTU Lo-fire, 825,000 BTU Hi-fire input,
    System = Early Dunham 2-pipe Vapor/Vacuum (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2
    Current connected load EDR= 1,287 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 8 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
  •  