Oil Tank piping help
-
Post a Reply to this Thread
Oil Tank piping help (4 Posts)
-
Oil Tank piping help
I'm having an underground oil storage tank removed and replaced with an above ground tank. The new tank will be located in the basement no more than 15' from a boiler with a Carlin 100CRD burner equipped with a suntec single stage pump. It is currently set up with supply and return piping.
My question. What is considered the optimum set up for fuel oil piping on a tank in the basement?
An oil delivery man mention going back with supply and return with a check valve on the supply through a duplex tank bushing from the top of the tank. Another tank guy mentioned using a single supply from the bottom of the tank. The new tank will be 275 gal.
A Suntec technical document stated that a single pipe is recommended, with no check valves, due to lower inlet line flow.
What is considered the accepted safe set up for oil supply piping for a tank on the same level as the boiler?
Thanks for any thoughts.
S. -
2 pipe
is not needed, and rarely is. If the system is now 2 pipe, make sure someone removes the bypass plug, and plugs off that port, ant there should never be any valve of any sort in a return line. At the pump or tank. The system will gravity feed the unit -
I second that
Bottom feed one line system is the simplest fix. But the ultimate bomb proof system is to top connect the feed out of a 2 to 1/2 bushing, followed by a vavle and a anit-sphion valve. Then a firematic fuseable link valve( for fire protection). Next a tiger loop at the fuel pump with two lines. This is idioit proof and you will never have a leak or worry in a fire. I run these setups with roth double wall tanks, if you spend the money on a double wall tank you should go all the way..........I;ve change hundreds of tanks, bottom feed granbys (we were ordering 75 at a time right from the factory). But think about it, if little johnnys swin;n his hockey stick around the oil tank and the valve breaks off bye bye 250 something gallons of fuel. Kinda stupid really, i've likely got 2500 12 gauge granby tanks out there and thats all it would take to have a major spill. -
Thanks
Thanks for the replies.