    venting oil and pellets (6 Posts)

  • dynamic dynamic @ 6:38 PM
    Contact this user

    venting oil and pellets

    I don't have a copy of NFPA211- Can I vent an oil boiler and a pellet stove in the same chimney ?
  • billtwocase billtwocase @ 6:42 PM
    Contact this user

    Why vent

    the pellet stove in a chimney? They sidewall vent normally
  • dynamic dynamic @ 6:47 PM
    Contact this user

    Hearth in middle

    My customer has a hearth in the middle of the living room. He is taking out a wood stove for insurance reasons and wants to add a pellet stove.
  • billtwocase billtwocase @ 8:11 PM
    Contact this user

    There should have been

    a separate flue, if the wood stove was legal, or installed to code. Are you sue that is a common flue?
  • Eric Eric @ 6:26 AM
    Contact this user

    I don't believe..

    there are any pellet stoves that are designed to vent into a chimney. You can drop a liner down the chimney for a pellet stove, but only if it is NOT serving any another applance.
    Read the manual from the stove, or call them and ask for their input.
  • Jack Jack @ 6:40 PM
    Contact this user

    pellet stoves are

    not negative pressure appliances. They have a positive pressure vent system. A chimney for your oil appliance is a negative pressure system. You cannot combine the two. As well NFPA 31 specifically prohibits solid fuel and oil venting into the same flue.
  •  