  • bman bman @ 8:24 PM
    Contact this user

    zvc pump problem

    I have a tacozvc-404-2 and trying to wire uponer two wire zone valves. my problem is that the zone valves open fire when t stat is calling but zone controll box dosent see that there open also how do you wire the circ pump to fire when zone is calling
  • Gary Jansen Gary Jansen @ 8:36 PM
    Contact this user

    ZVC reply

    Install a jumper across terminals 3 and 4 of the zones you have thermostats connected to. Wire 120 volt hot to one side of end switch, other side of end switch to pump. Neutral wire goes directly to pump. Set mode switch to normal. Priority switch to off. That should get you going. 
  • Tim McElwain Tim McElwain @ 7:12 PM
    Contact this user

    HI Gary Jansen

    it  has been a while since I have seen your name posting here, how are you doing?
  • Gary Jansen Gary Jansen @ 12:11 AM
    Contact this user

    Well Tim, it's like this

    I'm still fat and sassy
    I'm still living the dream
    and every day is a day in paradise!

    At least the 1st one is true.

    Thanks, Gary
  • Joe Mattiello Joe Mattiello @ 11:48 AM
    Contact this user

    zvc404

    The zvc404 is the facilitator for the multiple thermostats, and corresponding zone valves.  When the thermostat closes, TT close to energize the zone valve.  The end switch from the valve when wired to the 3, and 4 terminals communicates to the control the valve is open it's OK to fire the boiler and energize the system pump. 
     
    The system pump can be wired to the extra end switch.  the wiring schematic is found on the instruction sheet about midway down on the left hand side.  Hopefully this helps. 
    joe mattiello
  •  