The Wall
  • Post a Reply to this Thread

    TXV capacity (9 Posts)

  • edow edow @ 3:58 PM
    Contact this user

    TXV capacity

    What are the 3 factors that determine the capacity of a TXV?
  • Techman Techman @ 11:15 AM
    Contact this user

    TXV

    Are you talking theoretically? Or are you on a service call w/ a system that has a problem because the TXV is  r22 and the comp is r134a  and the Walk-In is warm  because the TXV is not feeding enough freon?!
  • edow edow @ 4:59 PM
    Contact this user

    TXV Capacity

    i am talking theoretically
  • Techman Techman @ 6:13 AM
    Contact this user

    Which

    ones do you know about?
  • Diamonds1 Diamonds1 @ 9:43 AM
    Contact this user

    Epansion Devices

    The three factors that determine the capacity of a TXV are theoritically
  • Tom Blackwell Tom Blackwell @ 4:47 PM
    Contact this user

    capacity modifiers

    1. Differential pressure across the TXV.
    2. Subcooling of the liquid.
    3. Superheat at the coil outlet.0
  • Diamonds1 Diamonds1 @ 9:41 AM
    Contact this user

    Expansion Devices TXV

    The three factors that determine the capacity of a TXV are
  • Diamonds1 Diamonds1 @ 9:41 AM
    Contact this user

    Expansion Devices TXV

    The three factors that determine the capacity of a TXV are
  • Empire Empire @ 9:08 PM
    Contact this user

    This sounds like a test......:-)

    I'll say Orifice size in valve, Delta" P" between hi and lo side and The temp and state of the liquid entering the valve...........

    I took a shot.  It's been a while since theory racked my brain......

    Peace

    Mike T.............
  •  
Post a Reply to this Thread