Forum / A-C, Heat Pumps & Refrigeration / Condenser fan motor?
  • Post a Reply to this Thread

    Condenser fan motor? (14 Posts)

  • Robert O'Brien Robert O'Brien @ 9:16 PM
    Contact this user

    Condenser fan motor?

    1075 RPM motor,has 2 speed taps,hi and low. What is the hi and lo RPM?
  • Ironman Ironman @ 11:36 PM
    Contact this user

    RPM

    Look on the data plate of the motor. The low is usually about 70% of the high. It is actually a horsepower tap more than a speed tap. With no load, the motor would run at the same speed on either tap. With a load attached (the fan), the motor slows down on the lower horsepower tap. This is why you should not increase the horsepower when replacing a multi speed motor.
    Bob


    You can choose to do what you want, but you cannot choose the consequences.
  • Techman Techman @ 6:13 AM
    Contact this user

    SPEED

    HI Robert, usually it's 850 rpm w/ 1075 as the hi
  • Eugene Silberstein Eugene Silberstein @ 9:37 AM
    Contact this user

    Right On!

    Lo speed will typically be between 750 and 850 on that motor. When in doubt, use a tachometer on the shaft to measure accurately, as all motors will vary somewhat.
    Eugene
  • Robert O'Brien Robert O'Brien @ 3:48 PM
    Contact this user

    Thanks!!

    Long story short,had a job yesterday with a bad condenser fan motor. All I had was a 1075  rescue motor,existing was 1/3 horse 825 RPM. At high speed,the new motor goes into overload fairly quickly. I assumed the fan was overloading the motor at the higher RPM,at set it to low speed with same result. Coil is clean and voltage good out of contactor. 
  • Techman Techman @ 4:41 PM
    Contact this user

    Motor

    Is the rotation  of the motorcorrect and the cond fan blade?What HP is the new motor at 825 rpm?
    This post was edited by an admin on July 3, 2011 5:51 PM.
  • don don @ 8:15 AM
    Contact this user

    Over load

    I dont see how the new motor could go into over load just bc u change the hp.Sound more like a bad run capacitor to me.
    Is this a three or four wire motor?
  • Robert O'Brien Robert O'Brien @ 11:40 AM
    Contact this user

    Right

    Right rotation,new cap. Can a fan designed for 825 overload a 1075 motor?
    This post was edited by an admin on July 4, 2011 11:40 AM.
  • Techman Techman @ 12:38 PM
    Contact this user

    RPM

    The new 1075 rpm motor is still running at 1075 rpm even on the lower hp tap,so the fan blade will overload the new motor.  Plus the cap size changes 208v vs. 230v You need the Rescue motor #5464 @ 825rpm
    This post was edited by an admin on July 4, 2011 12:40 PM.
  • Techman Techman @ 7:18 AM
    Contact this user

    Rescue motors

    How does one motor do it all? At pretty much the same speed [  hi 3/4 hp = 1110 rpm ,lo 1/5 hp=  1140 rpm ] Why not just use a 3/4 hp in all lower hp applications ?
  • Techman Techman @ 12:11 PM
    Contact this user

    Inverse Porportionality

    is the words the Emerson Motor Engineer used to describe what would happen to a 3/4 hp motor used in a 1/5 or 1/4 hp application.My motor repair shop guy said "The damn thing will overheat on you " The Rescue  condensor motor line has a "special" winding w/ two taps ,both @ 1075rpm ,but different HP's
    This post was edited by an admin on July 6, 2011 7:57 PM.
  • sasman sasman @ 9:45 PM
    Contact this user

    just a little read

    from Fasco Motor Facts

    FACT Modern multi-speed motors are really not multi-speed,
    but multi-horsepower. The speeds are simply taps at different
    points in the coil. The higher speeds are tapped at a point with
    fewer turns as compared to where the subsequent speeds are
    tapped in the same coil. The more turns that are wound before a
    tap is brought out, the lower the horsepower will be each time.
    Obviously, the lowest speed lead is connected to the end of the
    last turn on the coil. These added turns weaken the motor. This
    field weakening allows the load to slow the motor down each
    time a slower speed is selected. With no load mounted on the
    shaft, as with a bench test, no difference between speeds will be
    seen. If too strong a replacement motor is used on a unit, there
    may be no appreciable difference when the speed is changed in
    the unit. Remember, the motor relies on the load to slow it down
    between the speeds. As an example, if a 1/2 HP three speed
    motor is used instead of a 1/4 HP three speed, there might not be
    any noticeable difference between Hi, Med, and Low.
    NOTE: A motor nameplate showing 1350 RPM is a special design
    and must be replaced with an OEM direct replacement. This is a
    high slip 4 pole motor, which is not generally available in a general
    line of motors. If one is available, it would be marketed as an OEM
    direct replacement motor for a specific piece of equipment. These
    motors are specially designed for a very specific load.
  • Robert O'Brien Robert O'Brien @ 8:00 PM
    Contact this user

    The correct motor

    solved the issue,the 1075 was pulling over 5 amps at low speed,the motor is rated at 2.1 amps. I didn't realize a prop fan could be that different?
  • Robert O'Brien Robert O'Brien @ 8:00 PM
    Contact this user

    The correct motor

    solved the issue,the 1075 was pulling over 5 amps at low speed,the motor is rated at 2.1 amps. I didn't realize a prop fan could be that different?
  •  