  • kiwanda kiwanda @ 4:54 PM
    Contact this user

    Problem connecting PTAC to remote thermostat

    Still working on this PTAC in our addition:

    I'm trying to improve a marginal situation by operating an older PTAC
    with a remote thermostat rather than the unit's poor built-in controls.
    Little direction is available from Amana (Goodman) or the manufacturers
    of the two thermostats I've tried. Previously I had connected an old
    Honeywell T87F (round, mercury) t-stat that I'd removed from another
    location. It worked in cooling mode but not heat; it could not energize
    the fan circuit in heating mode. Rather than rig up something with a
    relay I decided to just grab a cheap modern t-stat that should work with
    the PTAC.

    Here's what I need to connect:

    -Amana PTC093A35AB PTAC; single stage cool, single stage electric heat (no heat pump)

    -LuxPro PSD011W thermostat

    The wiring diagram for the PTAC is on page 17 here: http://becketthvac.com/manuals/Amana/PTAC/service.pdf

    The diagram from the t-stat is page 2 here: http://www.luxproproducts.com/pdfs/P...G_Manual53.pdf

    Here's how I connected these:

    PTAC -->T-stat

    GH =G
    Y/W1 =Y
    W2 =W1
    R =R
    C =C

    But it didn't work. There is power to the t-stat, the fan will operate
    manually, but the PTAC does not respond to a call for heat or cooling.
    The idiot light on the control board signals either OK or thermocouple
    error. I should note that I've tried this with J2 on the T-stat set to
    "electric" and "gas" but neither work.

    Any thoughts on how to proceed? I called Amana, who sent me to Goodman,
    who left me on hold for 25 minutes. Haven't tried Lux yet, based on m experience with Honeywell they'll just send me back to Goodman.

    thanks,
    Kiwanda
  • cesar77 cesar77 @ 7:18 PM
    Contact this user

    cesar hvac

    first need to add a jumper between RH and RC in the stat,and set the stat to electric heat on a call for heat the fan will run and the electric heat.
  • kiwanda kiwanda @ 10:20 PM
    Contact this user

    » Problem connecting PTAC to remote thermostat

    It came with a jumper installed between RH and RC. Tried it with that jumped and set to electric. No dice.

    Thoughts? Should I check for voltage across Y and W with calls for heat/cooling to make sure the stat is working?  The control board on the PTAC flashes a "normal" code when not set to the remote stat, so I assume it's OK.

    -kiwanda
  • James Day James Day @ 11:47 PM
    Contact this user

    check voltage

    I would definately check voltage across the thermostat.  See if on a call for cooling and heat you get 24v to C  across Y and W.  If you are not getting voltage then the thermosat is not working.
  • Techman Techman @ 4:35 AM
    Contact this user

    PTAC

    Did you put the "t'stat/remote switch " in the remote position ?
  • kiwanda kiwanda @ 10:22 AM
    Contact this user

    Got it working, thanks!

    Checked the fuse, jumpers, and all connections and finally got this working last night. While troubleshooting the setup I
    must have fixed a bad connection; when I reconnected it all after testing the t-stat it worked.



    I think the problem was likely the silly design of the main board on the
    PTAC. Rather than a terminal strip it just has 14 pins coming off the
    board. There's a little plastic housing that slips over the pins, and
    you must insert jumper wires with spring clips into the slots for the
    appropriate connections. I removed and reinstalled those after checking
    the everything and it magically worked.



    I appreciate the help with this. After failing with the old Honeywell
    unit I was sure this new Lux would work fine. Glad it eventually did;
    it's already evident that having a real t-stat controlling this unit is
    far better than the primitive dial control it was delivered with. As a result I'm going to keep it for a winter (we see -25F here) and see just how much it will cost to heat the guest suite electrically before I decide whether or not to invest in a gas replacement.



    regards,



    kiwanda
  •  