    weil mclain wgo3 (8 Posts)

  • marsco marsco @ 6:52 PM
    Contact this user

    weil mclain wgo3

    just installed with beckett genesis control, lights, then control chatters, then locks out. did not contact becett yet. any ideas
  • lchmb lchmb @ 8:08 PM
    Contact this user

    connections

    Is the control going to lockout? Or chattering and shutting off completely..no light's visible..
  • billtwocase billtwocase @ 8:21 PM
    Contact this user

    chatter

    Could be a defective control, but I would check all wiring, voltage input reading, secure all grounds including case grounding, etc. It most likely has a low water cut off aquastat. What lights are lit on top? 
  • marsco marsco @ 7:10 AM
    Contact this user

    Wgo3

    I'm going back today to check. it does have a aquastat with a low water cut off
  • marsco marsco @ 7:26 PM
    Contact this user

    Solution?

    went back on job today, hooked up my contractors tool ,turned on power switch. no chattering. but 3 cycles showed pre time flame .I set up the burner and everything seems fine. Ran it threw a few cycles with the thermostats , it ran fine. Thanks for the input !
  • marsco marsco @ 7:27 PM
    Contact this user

    Solution?

    went back on job today, hooked up my contractors tool ,turned on power switch. no chattering. but 3 cycles showed pre time flame .I set up the burner and everything seems fine. Ran it threw a few cycles with the thermostats , it ran fine. Thanks for the input !
  • billtwocase billtwocase @ 8:30 PM
    Contact this user

    I would

    Check your clean cut pump. The stem was stuck open? Is it programmed for pre-purge?
  • Ron Jr. Ron Jr. @ 7:15 PM
    Contact this user

    Had some chattering

    after we accidentally spritzed a Genisys with water . Didn't want to take a chance so we just swapped it out .
  •  