Honeywell l7224u bad tempurature read
Problem with digital temperature on Honeywell l7224u. Not real happy with fit of probe in the well. Read is as much as 40 degrees too low at high end.
Have
you put the paste on the probe itself and pushed it in and pinned it per directions? I've never had one that far off unless there is an issue with the well or not properly installed. If you are saying this based on the Triadicator reading are you sure the guage is accurate??