    3 way diverter valve

    IM looking for a 11/4 sweat diverter valve full port that will divert water from the boiler to the distribution system,  To Solar tanks to the distribution system. The valve must shut down A port while opening B port.
  • Chris Chris @ 5:42 PM
    Contact this user

    How About

    A Taco I-Valve..

    http://www.taco-hvac.com/en/products/i%20Series%3Csup%3E%26reg%3B%3C/sup%3E%20Mixing%20Valves/products.html?current_category=184
    "The bitter taste of a poor installation remains much longer than the sweet taste of the lowest price."
  • radmix radmix @ 7:38 PM
    Contact this user

    I Valve

    The Taco I Valve is a mixing valve with outdoor reset. I have used these in the past. I need a diverter valve
  • Chris Chris @ 8:33 PM
    Contact this user

    The Have

    A setpoint version.
    "The bitter taste of a poor installation remains much longer than the sweet taste of the lowest price."
  • hot rod hot rod @ 8:34 PM
    Contact this user

    full port?

    how many gpm are you trying to flow? 3 way zone valves will be somewhere around 7.5- 8 cv. 3 way zone valves flow into the AB port and to either A or B port. Motor open, spring close.

    There are 3 way ball valves, diverting or bypass. In one position you have a full port flow, when the ball rotates the flow is around the edge. so the Cv is different depending on which port is open.

    With a 3 way zone valve the Cv is the same in either direction.

    hr
  • Plumdog Plumdog @ 8:49 PM
    Contact this user

    Let me know

    if you find something like that...so I can use it to switch between DHW and Heating without using two pumps and check valves. Could be done with two White-Rogers 11/4 zone valves, but for the cost and labor you might just as well use two pumps and checks.  
  • radmix radmix @ 6:53 AM
    Contact this user

    diverter valve

    I need 6 gpm for the proper flow for a primary loop on a triangle tube boiler. I was looking at the Caleffi Solar manual but the diverter valve only goes uo to 1".
  •  