    return duct into back of furnaces (5 Posts)

  • Paul Paul @ 9:41 AM
    Contact this user

    return duct into back of furnaces

    i have seen a few warm air furnaces where they didnt come into the left or right side of furnace for return air duct connection,instead they cut a hole in rear of furnace. every manual i have looked at the manufacturer says a big no to this. i am curious if anybody knows why and what it does or doesnt do to the furnace life or operation.
  • add add @ 10:24 AM
    Contact this user

    hi-boy /low boy

    there is different types of air furnaces. what is exactly that you are looking for?
  • Paul Paul @ 6:46 PM
    Contact this user

    highboy

    hi boy furnaces
  • John Mills John Mills @ 8:43 AM
    Contact this user

    No

    Check the manufacturers instructions. I'd guess  you'd really be hurting on airflow doing it that way since the air would hit the back of the blower housing and be greatly restricted. As short as today's furnaces are (I know, coils are tall) build a box under the furnace and come in the box. 
  • Big Ed Big Ed @ 11:34 PM
    Contact this user

    Hazard of open blower cabinet ....

    The blower and fuel combustion would be fighting for the same oxygen ...Improper combustion creates CO .

    The open blower cabinet will cause a negative pressure in furnace room countering the pressure drop needed for properly venting combustibles to the outside ...

    The free wheeling blower without the resistance of a return duct will blow less air and increase amp draw.....

    Less air would increase temperature diff across the
    heat exchanger , eventually burning a hole in heat exchanger ...

    Higher amp draw , could blow a fuse , burn up controls , motors and wires ...
    I have enough experience to know , that I dont know it all
    This post was edited by an admin on December 30, 2011 11:39 PM.
  •  