    Warren Webster trap? (7 Posts)

  • Jeff Elston Jeff Elston @ 10:31 AM
    Contact this user

    Warren Webster trap?

    Are these still available? Or a replacement?
    This post was edited by an admin on December 21, 2011 10:33 AM.
  • crash2009 crash2009 @ 6:48 PM
    Contact this user

    Webster

    I have read other threads where others have recomended  http://www.tunstall-inc.com/?s=webster
  • gerry gill gerry gill @ 7:18 PM
    Contact this user

    out of business- sorry

    Like Crash said, use a tunstall or a barnes and jones repair kit.
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.
  • Jeff Elston Jeff Elston @ 9:34 PM
    Contact this user

    Thank you

    Any tips on Identifying the trap ?

    I didn't see and other markings.  
  • Gordo Gordo @ 9:39 PM
    Contact this user

    I Hope for You

    that the numbers are on the body somewhere underneath all that paint.  It may be something like "533"

    Is that trap being used to drip a large steam main perhaps? 
  • Jeff Elston Jeff Elston @ 10:38 AM
    Contact this user

    trap is on Radiator

    It is a bank building in center city Philly.  A train wreck ,,, the trap is on a radiator its a warren Webster system the boiler was sitting at 5psi when i got there the water was squirting out of the vents !  steel hammers were doing there thing.   Paint was thick. thanks again
  • Gordo Gordo @ 11:20 PM
    Contact this user

    The number should be on the trap body

    somewhere...usually on the side you can't get to.

    It may be a 7 series trap.

    Yeah, 5 psi is not enough...if they want to MOVE the building.  500 psi would do it.
    5 oz/in2 is all that's needed to HEAT that building.

    Were the squirting vents on the radiators perhaps?
  •  