    Old Steam system (5 Posts)

  • George75 George75 @ 5:17 PM
    Contact this user

    Old Steam system

    I have an old steam system that has been converted to district how water.
    .
    system has a nice old pipe system, they added a circulator to the system, (cast iron radiators).

    The question is the piping on the radiators, They piped it so the hot water enters the bottom and exits the top.
    .
    Seems like you would be fighting gravity.
    .
    What is the proper way to pipe these?
  • JStar JStar @ 7:50 PM
    Contact this user

    RE

    Not a huge concern. Ideally, the supply should enter the top, and exit the bottom. In a pumped system, there is no longer any gravity working on the water. Are the radiators heating properly?
  • George75 George75 @ 9:20 AM
    Contact this user

    Re old steam

    They have some balance issues, using Danfoss valves, but I will check on flow if this piping is ok.

    Thanks,
  • George75 George75 @ 9:20 AM
    Contact this user

    Re old steam

    They have some balance issues, using Danfoss valves, but I will check on flow if this piping is ok.

    Thanks,
  • Charlie from wmass Charlie from wmass @ 9:59 PM
    Contact this user

    It is not ideal but it will function

    There is a slight loss in heating rate when piped this way.
    Cost is what you spend , value is what you get.
  •  