The Wall
Forum / Oil Heating / beckett nx burner
  • Post a Reply to this Thread
    beckett nx burner (3 Posts)
  • john18064 john18064 @ 7:46 PM
    Contact this user
    beckett nx burner
    Had an issue today with a beckett nx burner firing at .50x60a mfgs specs for a Carrier Low Boy furnace. the Flame was very irratic and the retention head was soaked of oil. what would cause this. tried air settings, retention settings, changed nozzle, no avail. R.W. Beckett says change from a .50x60a to a .50x60w.
  • lchmb lchmb @ 4:40 PM
    Contact this user
    Did
    you zero out the drawer assembly? Replace the filter and strainer to make sure they werent plugged? Check oil pressure? What was your draft, I believe the NX likes about -.02 and anything higher will cause erratic fire...
  • Mac_R Mac_R @ 8:46 AM
    Contact this user
    NX
    The NX is a high static pressure retention head burner.  It likes a +.02 and will fire up to a +.05 without problem.  I would checkout the nozzle seat.  make sure the adapter is not scored and the nozzle has not been over tightened.