chloride level
I was about to have a Buderus SST stainless steel DHW intalled which use 316 SS and 304 SS on the HX. The mannual said not to exceed 80 ppm of chloride. I had Analytical Balance test my water for chloride level since my town in Randolph, MA are not required to test for chloride, the result is 91mg/l which is 91 ppm. What do you think I should do?
-
make sure that there....
is an anode rod in the tank and change it out yearly.
-
Bradford White RTV series
Or a Bradford White RTV Stainless steel tank made out of 444 stainless steel which is apparently nearly immune to chloride attack ( much better than 300 series stainless steels).
-
Bradford White RTV series
dp
This post was edited by an admin on January 17, 2012 11:01 AM.
-
thanks
Thank for the feedback. I had considered Bradford White RTV SS. My boiler is going to be Buderus G125 with logamatic, any problem using a different brand indirect.
-
just make sure....
the probe for the logamatic can fit in the aquastat port.
-