Backflow preventers
My customer has a gas fired steam boiler with a condensate tank. The rpz drips water and now the boiler is short cycling. I have the pressuretrol set at 6 psi and its reaching that quickly. Any input would help. I'm confused
First...
I would recommend that you move this thread to the"Strictly Steam" forum. You'll get more responses there.
Second, set the pressuretrol down to 1 psi or less. The system doesn't need any more than that and setting it too high actually causes it to heat slower and creates other issues.
Bob
You can choose to do what you want, but you cannot choose the consequences.