    burner got wet (7 Posts)

  • TeachMeSteam TeachMeSteam @ 4:16 PM
    Contact this user

    burner got wet

    I have a commercial steam boiler. Somebody took a water hose and completely hoses down the boiler and burner. Its dripping wet now. I am thinking it shouldn't make a difference but is it safe to start the boiler?
  • Steve Whitbeck Steve Whitbeck @ 5:22 PM
    Contact this user

    wet burners

    I would suggest blowing out the burners and pilot assembly or you may get a supprise delayed ignition. I have cleaned many a boiler with a garden hose if there was a floor drain close. ( I always took the burners out though)
  • Jamie Hall Jamie Hall @ 7:06 PM
    Contact this user

    If they also

    managed to hose down the electrics -- particularly circuit boards or things like that -- make sure they are completely dry before you try to do anything.  Electricity and water don't mix very well...
    Jamie

    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.

    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • JStar JStar @ 6:29 AM
    Contact this user

    RE

    Anything that got wet needs to be replaced. I've seen equipment "dried out", then a week or a month later, it caught fire, exploded, or just stopped working. Don't take a chance.
  • Steve Whitbeck Steve Whitbeck @ 7:07 PM
    Contact this user

    Jstar

    Only the electronics would need to be replaced - The burners are fine IF they are dried out.
  • JStar JStar @ 10:04 PM
    Contact this user

    RE

    I might agree with you on the burners if they are stainless steel, but I've seen burner manifolds and black iron rot from the inside out after weeks of being "dry". And pilot orifices aren't very tolerant of debris.

    Safety over sorrow. Always.
  • Steve Whitbeck Steve Whitbeck @ 10:25 PM
    Contact this user

    Jstar

    I have been cleaning sooted up boilers with water for years ( 36 ) and have NEVER had a single isue. ( I have about 20 customers on well gas ) I always blow out the pilot and burners before I reinstall them. The pilot line should have aluminum tubing so there won't be any rust in that line.  Some manufacturers actually suggest cleaning the heat exchanger with water...
    This post was edited by an admin on January 25, 2012 10:27 PM.
  •  