    Outdoor venting termination

    The hot water boiler installation manual reads that the sidewall vent termination for a gas fired boiler needs to be a foot from the ground plus expected snow height.  What's the minimum height from the ground that an exhaust vent can terminate in the Greater Boston area?

    The manual also states a minimum distance it must be from an inside corner, but not a bay window.  How far should the vent be from a bay that originates at ground level?
  • furnacefigher15 furnacefigher15 @ 8:49 PM
    Contact this user

    Snow line

    3 feet from any window I believe. I would treat the bay that goes to the ground like a corner. Wind can cause an eddy current which can screw up the draft.

    Snow line. How much snow do you get?

    Is the vent planned in a location where snow might drift?

    How high off the ground is the gas regulator by the meter?
  • ed wallace ed wallace @ 10:44 PM
    Contact this user

    Outdoor venting termination

    In boston Ma area i would put it at least 3 ft above ground level field controls now sells a power venter that is raised about 3 ft off the ground to be used to replace a chimney
  • ed wallace ed wallace @ 10:45 PM
    Contact this user

    Outdoor venting termination

    In boston Ma area i would put it at least 3 ft above ground level field controls now sells a power venter that is raised about 3 ft off the ground to be used to replace a chimney
  •  