The Wall
Forum / Domestic Hot Water / expansion tank location with tankless heater
  • Post a Reply to this Thread
    expansion tank location with tankless heater (2 Posts)
  • Brain Ross Brain Ross @ 8:04 PM
    Contact this user
    I'm installing a noritz tankless dv hot water heater with noritz's hot and cold isolation/pruge valves. Since the valves attach to the tankless with half unions there is no place between the cold valve set-up and the tankless to cut in an expansion tank.
    Should I then install the expansion tank between the prv and the iso/purge valve set-up. I have always been under the belief that the expansion tank should be installed before the cold water shut-off incase the valve is closed it would still absorb any expansion without activating the prv.
  • Mark Eatherton Mark Eatherton @ 10:13 PM
    Contact this user
    I wouldn't put one in....
    It's a tankless, which means it won't be firing unless a tap is open. Expansion tanks are there to allow the expansion to be absorbed. You won't have any expansion to speak of, because if the burner is on, a tap is open. When the tap is closed, the burner is off.
    Save your money for something else.
    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
    This post was edited by an admin on January 26, 2012 10:14 PM.