Hot Water Boiler
Replacement Hot Water Boiler-with cast-Iron Radiators 2 pipe
Boiler is piped reverse return-Radiators on second floor do not seem to want to get hot-bleed and bleed -but get mostly water-first floor is hot
System has grundfos 26-99 pump on return
Any Thoughts-suggestions would be appreciated
System pressure is 20#
Sounds like....
a gravity conversion. How is the near boiler piping. the 26-99 is WAY too big. more like a 15-58 on low speed/ spd1.