    Expansion Tank Pipe Size (3 Posts)

  • 152NP 152NP @ 1:24 PM
    Contact this user

    Expansion Tank Pipe Size

    Can anyone tell me how to correctly size the piping connecting an expansion tank to the system?  I am currently installing a 40gal tank on a 130,000 Btu system. Water temp in the boiler loop where the tank will connect will be 190, and the tank will be charged to 19psi.. The tank comes with a 1 1/4 inlet, which got me wondering. I figured I better check with those than know more than be before bushing this down to 1/2 in to connect to a spirotherm. The tank is large to accommodate a three story building with cast iron radiators, and to work with a solid fuel boiler without using a dump zone.
  • Mark Eatherton Mark Eatherton @ 2:39 PM
    Contact this user

    1/2" should be fine...

    The velocity of the expanding fluid will be nil.

    The diaphragm is made for he temperatures and pressure it will be seeing, so no benefit to running a larger pipe to dissipate heat before it sees the bladder.

    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • 152NP 152NP @ 3:31 PM
    Contact this user

    Expansion Tank Pipe Size

    Thanks for the info. That is what I thought, but sometimes what seems to make sense to me turns out to be wrong for some unforeseen reason. I figured it was best to check with someone when potential safety is involved.
  •  