Forum /
Strictly Steam /
water being pulled from boiler
Post a Reply to this Thread
water being pulled from boiler (5 Posts)
I have a 450 mills smith boiler ,2,500,000,btu 2 pipe condensate pump return that the water is pulled right out of the boiler and going off on low water. -
Has this problem just started?
Has it always done this? If not have there been any changes to your system lately?
Is it piped properly? You may need to post a few pictures of the boiler and near piping if you're not sure.
Anything done with your boiler water lately? Could be foaming and priming? -
Need more info
Just trying to narrow things down a bit.
Does the water disapear, never to be seen again? (which would suggest a leak)
Or, does the water eventually make its way back to the boiler? (which would suggest pressure too high, or a condensate return problem)This post was edited by an admin on February 8, 2012 9:27 AM. -
more questions
Does the water suddenly disappear? Does the system have a condensate tank and pump? Are there zone valves on any of the steam mains?Dave in Quad Cities, America
http://grandviewdavenport.com -
Disappearing water
I will assume the boiler has worked well in the past and nothing mechanical has been changed. The boiler water has three ways to get out of the boiler: Carryover from dirty water and surface tension, it can back out the bottom of the boiler through a defective check valve at the condensate pump and up the chimney if you have a leak in a section.
I have had a lot of good results by cleaning the water side of the boiler.
Good luck,