    Expansion tank issues (74 Posts)

  • KCA KCA @ 9:33 PM
    Contact this user

    Expansion tank issues

    Hi Everyone...

      Take a look at the drawing...  While the boiler is running at +- 18psi, all on a sudden within 2-4 seconds the pressure raises to 30psi and blows the pressure relief.  Temperature doesn't appear to have any bearing....  Not sure what does....  The system acts as if expansion tank " isn't there....  I temporarily installed Expansion tank "B" and all is well...  Even if I turn expansion tank "A" off so it acts as if "A" weren't there.. .    I have switched tanks with Expansion tank "A" and it doesn't matter....  So I believe that Ex tank "A" is good...
    I have the indirect shut off both the coil & the domestic.
    This happens when the temp is 180degF or 120degF...  doesn't matter.
    It seems that installing the expansion tank "B" solves the problem..  which is great but I wanna know why...  :)
    Questions:
    1.  Why am I getting pressure spikes? in the first place...
    2.  Why doesn't expansion tank "A" seem to be seen by the system?
    3.  How come installing expansion tank "B" solves the problem even with "A" off?

    I've rounded the system off to be +- 18 gallons...
    Expansion tank "A" = Extrol #30
    Expansion tank "B" = Extrol #30

    Oh...  one other thing...  I didn't install the system...  I'm just there to fix it..  :)

    Thanks for all your help!!  I really appreciate it...

      :-)  KCA
    This post was edited by an admin on March 2, 2012 9:35 PM.
  • furnacefigher15 furnacefigher15 @ 10:28 PM
    Contact this user

    Because

    You are pumping into the boiler.

    When there is some more distance between the tank and the pump the pressure will drop a little more between the tank and the boiler pump then it did before, causing a lower output pressure from the boiler pump.

    If you don't need 18 psi, lower the pressure.
  • Ironman Ironman @ 10:39 PM
    Contact this user

    Move The Tank...

    And the SriroVent into the primary loop where the flow switch is located. The way it is now, the PONPC is in the secondary.

    Pumping into the boiler is the proper method with this arrangement as long as the boiler pump is downstream from the PONPC.
    Bob Boan



    You can choose to do what you want, but you cannot choose the consequences.
  • LarryC LarryC @ 11:00 PM
    Contact this user

    You are making steam.

    " While the boiler is running at +- 18psi, all on a sudden within 2-4 seconds the pressure raises to 30psi and blows the pressure relief.  Temperature doesn't appear to have any bearing.... "

    I am guessing you are making steam in the boiler.  The expanding steam bubble raises the pressure and pops the relief. 
    Is a Taco 014 a small pump?  Is that pump recommended for the boiler circulator in a primary secondary set up?
    If that is the correctly sized pump, then I would look for a hot spot.  Perhaps a blocked water passage, improper firebox conditions, or improper flame size.

    Be aware I am not a heating professional and my advice is worth exactly what you paid for it.

    Good Luck.
    This post was edited by an admin on March 2, 2012 11:01 PM.
  • icesailor icesailor @ 12:50 AM
    Contact this user

    Checks & Balances:

    If those circles with diagonal lines denote check valves next to the secondary loop, the fill is in a locked loop between two check valves, the second being the rotten IFC's in the check valves. It you had a real wet head check valve, you would be able to manually open the check and see if the problem would stop. As it is, you can't. The first tank, tank "A" is being hydraulically isolated from the system and the system can't "see" what the tank (A) is doing. Not so with tank "B". It is on another side of the rotten IFC's.
    It seems to me but I can't "see" the drawing that well.
  • KCA KCA @ 4:23 AM
    Contact this user

    The system is piped

    according to Weil McLain specs...  The circulator 0014, is actually shipped with the boiler...  It's a pretty big head circ..  I'll grant that the secondary lines are too small...  But that shouldn't matter with regard to the ex tank...  The pressure differential between the two pressure gauges on either side of the Taco 0014 is +- 3 psi...

    I always like to put the spiro & expansion tank in the primary but....  It doesn't have to be...  It would seem that the ex tank "A" can be seen from any part of the system..  So why doesn't it act that way?

    The valves off of the primary & on the secondary branches are ball valves..

    The pressure at 12 would do the same as 18...  except that you need at least 14 for NPSH and now Taco requires 20 for systems above 5000 feet...  so..  18 seems like a good middle of the road number...  I don't agree with the 20psi requirement.....

    :-)  KCA
    This post was edited by an admin on March 3, 2012 4:29 AM.
  • Paul48 Paul48 @ 8:13 AM
    Contact this user

    NOT

    piped to W/M's specs at all.
  • KCA KCA @ 10:41 AM
    Contact this user

    Here is a drawing

    from the WM manual...  It's piped like this..  I left the sidearm out because I isolated it during this issue...  and the flow check isn't installed..

    KCA  :-)
    This post was edited by an admin on March 3, 2012 10:47 AM.
  • Mark Eatherton Mark Eatherton @ 9:35 AM
    Contact this user

    What happens if you shut off the make up?

    What you are seeing is what Siggy calls "droop". With the pipes being undersized between the Primay and the secondary pumps, when they kick on, they create a significant drop, or droop in pressure that the PRV sees and sends water in. Moving the PONPC to the secondary circulators inlets, or as close as you can get it to that point should stop the problem. The exp. tank doesn't HAVE to be connected at the air separator.

    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • KCA KCA @ 10:25 AM
    Contact this user

    I shut the PRV off Mark...

    I thought of that and killed the make up..  But that's a good idea...  :)

    :-)  KCA
    This post was edited by an admin on March 3, 2012 10:48 AM.
  • SWEI SWEI @ 9:53 AM
    Contact this user

    Overpumped?

    3 PSI is about 7 feet of head, at which a 0014 moves around 26 GPM.  At full output at sea level, the Ultra 230 should give you 14 degrees of delta-T (and as it modulates that number will drop.)
  • icesailor icesailor @ 10:03 AM
    Contact this user

    Pressure Issues:

    The pressure at 12 would do the same as 18... except that you need at least 14 for NPSH and now Taco requires 20 for systems above 5000 feet... so.. 18 seems like a good middle of the road number... I don't agree with the 20psi requirement.....

    Funny thing about that pressure thing. I was talking to a gas and heating professional that does a lot of troubleshooting about such things. I told him about raising pressures on systems where there were high parts in systems and air being sucked into can or auto vents. I don't remember when this conversation occurred. Last week, he told me that after I told him that, he went to their office and raised the pressure to 20#, For 17 years, the air handler in the attic of their two story building would get air bound, and for 17 years, he would need to go up there multiple times during the heating season. Since he raised the pressure to 20#, he hasn't had to go up and vent it once.
    I remember things like that.
    Do you understand why you need to raise the pressure above 5000 feet? There's an explanation
  • KCA KCA @ 10:34 AM
    Contact this user

    That doesn't have anything to do

    with a circulator....  They want 20psi on the circs...  They usually are around the mechanical room...  I was told that it was because flashing in the cartridge...  But why 20psi & why above 5000ft?   That is something else altogether..  But thanks for bringing it up..

      :-)  KCA
  • icesailor icesailor @ 12:15 PM
    Contact this user

    Lotteries:

    Bingo !!
    You hit it on the head. "Flashing in the cartridge." Flashing into what? STEAM.
    Try resettng the pressure to 20# and then turn on the boiler. If the problem goes away, it's the pressure. All those pumps trying to do their thing can and will become willful children and creat havoc in the system.
    Do you understand need to raise the pressure in the system when the system is at a higher level above sea level?
    Its important.
  • KCA KCA @ 4:34 PM
    Contact this user

    No I don't

    Explain why you should have 20psi in the system when it's over 5000 ft ASL...

        I don't know...  :)

       KCA  :-)
  • Zman Zman @ 10:21 AM
    Contact this user

    Keep us posted

    This is an interesting one. I think Mark is on to something, although I would expect the problem would occur on pump shutdown. The flashing to steam would make sense but only if you were pumping away from the high head loss boiler.
    Icesailor, could you please explain pressure over 5000 feet? Since the pressure is relative to the atmosphere,I am not sure what you are saying. Your example of air locking makes sense. You should have the pressure from the building height + a safety margin. The building you describe would need 15 to 20# depending on the height.
  • icesailor icesailor @ 12:33 PM
    Contact this user

    As I see it,

    As "I" see it, 0 (zero) PSIG at Sea Level isn't the same as "0" at 5000 feet. Therefore, when the water in the system gauge says  "0" at 5000', it isn't the same as "0" at sea level. Therefore, the boiling point is lower at 5,000 feet.
    On Mt Everest, climbers have a lot of difficulties. One is that a lot of food needs heat to release nutrients that the body can take up. The product may need to be heated to 175 degrees for the nutrients to be released. Especially in dried or dehydrated foods. But water may be boiling at 150 degrees at higher altitudes. You can't get the water/liquid hot enough without it all boiling away.
    Taco is recognizing what some of us have felt for years that cavitation in pumps was a big problem. But we are considered "contrary".
    Consider this. If you had a system that you filled to 12# PSIG, and you moved the entire system to Denver Colorado without opening it up, what would happen to the pressure?  (Hint: It doesn't go down.)
    What happens to a system filled to 12# PSIG Gauge in Denver Colorado and you move it to The Island of Long?  (Hint: It doesn't stay the same.)
    As I see it.
    Those climbers on Mt Everest could put their food and water in a pressure cooker. But if they tried to open it, it would explode if the water temperature was higher than the outside pressure keeping the boiling point down.
    Isn't this sort of how vapor/vacuum steam systems work?
  • Zman Zman @ 12:45 PM
    Contact this user

    Altitude

    Boiling point at 10,000 feet is around 190 degrees. It does effect cooking and requires boiler temps to be set a bit more cautiously. I agree that the system pressurized at one altitude and moved to another would read differently. However if you charge the tank and fill the system at a given altitude, What is the difference? Perhaps ME will weigh in on this?
  • KCA KCA @ 4:36 PM
    Contact this user

    PSIG

    is the same at sea level or at 5000ft above...  PSIA is different...

    Boiling point at 15psiG is the same at sea level and at 5000ft above... 

        :-)  KCA
    This post was edited by an admin on March 3, 2012 4:38 PM.
  • bob bob @ 9:48 PM
    Contact this user

    PSI

    KCA, Question . if you hook a manometer up to a gas burner at sea level and it reads 3.5"WC and do the same in Denver and it reads 3.5" WC is the pressure in the burners the same?
    bob
  • KCA KCA @ 10:52 PM
    Contact this user

    I think what you are asking is....

    Does a manometer (and I'm assuming that we're talking about a digital one) take into consideration atmospheric pressure in the readout...  I don't believe so... I believe that a manometer reads out in PSIA...
     Regardless manifold pressure isn't a closed system...


    Interesting question I had to think for a minute...  So that means that the answer may not be correct...  Lol...

     :-)  KCA
    This post was edited by an admin on March 3, 2012 11:01 PM.
  • bob bob @ 12:36 AM
    Contact this user

    Pressure

    The pressure in the sea level burner is 14.825 PSIA the pressure in the Denver burner is 12.325PSIA that is why the btu content of nat. gas is 830 /Cu Ft in Denver and 1040 at sea level. Manometers use atmospheric pressure as a reference just like pressure regulators.
    I use to wonder if bourdon tube gauges used atmospheric pressure as a reference so I took two high quality 0 to 10 Lb. gauges at sea level both reading zero and capped one. I drove to Denver, the capped gauge read 2.5 Lbs the un-capped read zero. Two boilers one at sea level one in Denver both with gauges reading 12 Psi will have different boiling points.
    bob
  • KCA KCA @ 12:42 AM
    Contact this user

    PSIG

    OK...  I looked it up and here is what I found..

    PSIG is the pressure read from a gauge which reads the difference
    between the pressure in the pipe and the pressure of the atmosphere.


    PSIA is the total pressure including the pressure of the atmosphere.

    That being the case then you are right...  the water at at 12psig at sea level would boil first......

    I thought that PSIG was the pressure in a pipe read from a gauge regardless of atmospheric pressure...   I knew that PSIA was ...  what it says...

    :-)  KCA
    This post was edited by an admin on March 4, 2012 1:04 AM.
  • Zman Zman @ 10:57 AM
    Contact this user

    Water off?

    Sorry I did not see you had tried to turn off the water. Was the expansion tank functioning correctly with the water off, of was the level changing? Have you tried isolating the secondary loop and just running the boiler loop? It seems the problem must be related to the 0014 in relation to the high head boiler. I assume you have triple checked your pump directions?
  • KCA KCA @ 11:05 AM
    Contact this user

    Yeah..

    I triple checked the direction...  & I've isolated the secondary..  to a point..  Because the expansion tank is there..

    :-)  KCA
  • Zman Zman @ 11:19 AM
    Contact this user

    Photo

    Humm! Do you have a photo. Maybe there is something you are missing that someone on here can find? Double check valve?
  • Zman Zman @ 11:19 AM
    Contact this user

    Photo

    Humm! Do you have a photo. Maybe there is something you are missing that someone on here can find? Double check valve?
  • KCA KCA @ 11:27 AM
    Contact this user

    That would be great

    but the mechanical room is like...  5' across by 6' deep & it has (besides the boiler & sidearm & secondary..)  two gas fired furnaces..  as well as a whole house filtration (hepa) system...  so I couldn't get a good pic...  Some of the pipes are up in the joists..  etc...
    There has got to be something that I'm missing...  I even thought that the diaphragm was stuck to the inside of the ex tank so I changed it...  No difference..
    You can see the ex tank "A" from everywhere in the system..  so I don't understand why it doesn't work..  Yet installing one in position "B" works great..  Hmmmmm....  I guess I may never know..  But then what a waste of time...

      I appreciate everyone wanting to help...  You're great..

      :-)  KCA
  • Steve Whitbeck Steve Whitbeck @ 12:02 PM
    Contact this user

    tank

    What is the pressure on EXP A when the boiler pressure is at 0  ???
    Try installing tank B where tank A is now and plug the fitting for tank B.
    You may just have a bad tank. Piping shouldn't be a problem.
  • icesailor icesailor @ 1:00 PM
    Contact this user

    Extrol Tank Precharge:

    That's easy enough to check without doing that. Drop the system pressure to zero and check both tanks with a tire gauge. They both should show pressure and the same amount..
  • KCA KCA @ 4:32 PM
    Contact this user

    The Ex Tank "A"

    is at +- 18psi when system is at 0psi....  I already tried exchanging tanks with tank "A"...  The tank is OK...

      Thanks for the thoughts...

       :-)  KCA
  • icesailor icesailor @ 1:21 PM
    Contact this user

    Heating Extrols Vs Well Extrols:

    I've not seen this answered.
    On Well Extrols, the instructions tell you to set the tank pressure at 2# PSIG below the "Cut-In" pressure . Ie: If the cut in pressure is 20#, (20/40# pressure switch) set the tank pressure at 18 PSIG. Cut in at 30#, (30#/50# switch)  set it at 28#. I find that it is better to set them at 3 to 5 pounds below the cut-in pressure to stop any possibility of the water stopping while the pressure switch closes, the pump starts and the water gets going. I can't remember how many years I have followed this rule. But it was shortly after the first complaint of the water pausing while the pump built pressure.
    If you look on the Amtrol Website, there are no instructions on what to set the pre-charge pressure to for heating Extrols. We are left in the wilderness.  And the instructions in the box is no different. To my aged and deteriorating brain, the heating Extrols come pre-set at approximately 12#. If the system pressure is at 15#, you have a 3# cushion. If it is at 12#, you have no cushion. If you set the system pressure to 18#, you have a 6# cushion. It is suggested by some to raise the precharge to equal the system pressure. That would give you no "reserve" if the system cooled and the system water contracted.
    On systems I see with air problems, the PRV is usually stuck and the system is 10# or below. Hit the by-pass and the system may not ever stop filling.
    If the system is precharged to 12# and you run the system pressure at 18# with a 6# differential, it works fine and you have more room for expansion.
    On a well Extrol you cannot set the pressure the same as the cut-in pressure. It must always be lower than the cut-in pressure. Why is this not so in a heating system?
    An inquiring mind is asking.
  • furnacefigher15 furnacefigher15 @ 2:12 PM
    Contact this user

    Well verse heat diaphragm tanks

    They are not doing the same job.

    A well tank uses the air cushion to stabilize water pressure, not to account for thermal expansion.

    The reason the heating diaphragm tank should be set the same as the water pressure is to maintain a place for the water to go.

    At balanced pressure the diaphragm will have not allowed any water into the tank.

    Once there is more water pressure then air, water will push into the tank.

    If you start out with a lower tank pressure then fill pressure, then there will be less room for the water to expand because it has already started to fill the tank before it even got hot. The result is a reduction in the capacity of the tank.

    If the pressure of the tank is high then the system, the result will be that the expansion tank won't accept water until the water has heated and pressurized enough to match the pressure of the tank.

    So the thing to do is match the pressures, that way the water will have a place to go when it heats and expands, and the tank will have its full potential for expansion capacity.
  • icesailor icesailor @ 11:44 PM
    Contact this user

    Air Head:

    When you take a Well Extrol or a Heat Extrol out of the box, and it is precharged to whatever it is precharged, the pressure inside the bladder has pushed  the bladder to the bottom of the tank. It is pushed off when the incoming pressure is greater than the pre-charge. There is no pressure range when the pre-charge is higher than the set system pressure. In Hydraulics, the difference between zero and 100# is a drop. It can't be compressed. The fill valve will add water, like the water on  a pump will stop.
    But that's not the cause of a problem you didn't create and are trying to solve.
    Did the original installer make the closely spaced tees 4 pipe diameters?  That's 5" center to center on the 1 1/4: primary loop. A 6" nipple isn't 4 pipe diameters. The closer the tees, the better the mixing. If you don't get good mixing in the zone between the tees, you may not get as much return water as you need to keep the boiler cool.
    Its not the tanks.
  • KCA KCA @ 11:49 PM
    Contact this user

    The space between the tees

    is about 5" I would guess...  He used a 3" nipple on two 1 1/4 x 1" tees so they are close...

    :-)  KCA
  • icesailor icesailor @ 1:30 PM
    Contact this user

    Spaced Out:

    KCA,
    Does the primary/secondary loop configuration in this system that you did not install conform to this?
    Note especially the part about distance for closely spaced tees AND the distance from the closely spaced tees to turning ells?
    It does make a difference.

    When using an iSeries-R Mixing Valve, the following piping requirements
    must be considered for proper operation.
    1. In order to hydraulically isolate the boiler loop from the injection or system
    loop primary/secondary piping must be used. There must be no
    more than 4 pipe diameters between the tees in the boiler loop (Note 1).
    2. There must be at least 6 pipe diameters of straight pipe on either side
    of the tees (Note 2) in order to prevent the momentum of water in the
    boiler loop from pushing flow through the injection loop.
    3. There should be a minimum of 1 foot drop on the return pipe of the
    injection loop, in order to create a thermal trap (Note 3) and prevent
    unwanted heat transfer.
    4. When using a 2-way iSeries-R Mixing Valve, a balancing valve must
    be located between the tees in the system loop, in order to provide a
    pressure drop to induce flow through the mixing loop.
  • KCA KCA @ 4:51 PM
    Contact this user

    When I run an injection

    loop...  I tie into the space between the expansion tank & the primary circulator...  You excape the ghost flow issues as well as the primary pump pushing unwanted water into the injection loop..  Has always worked well for me..

      Just an FYI

     :-)  KCA
  • icesailor icesailor @ 1:41 PM
    Contact this user

    Another thing on that boiler/system.

    Here's another thing on that system. It is becoming common knowledge where I work that they are often way over fired in some applications. If anything is incorrect in the piping, and you have diminished flow through the primary loop and by diminished flow, I mean returning cooler water going into the boiler, it will do what you describe, flash into steam. I have a friend who is constantly down-rating these boilers because they are too big and you can't get enough flow through them to cool them. Once they start to steam, the flow stops.
    A question for Steamhead, if a teapot boiler starts to steam, will the circulator pump be able to push the "bubble" out? Wondering.
    Why I like Low Loss Headers or Hydraulic Separators better than improperly spaced and installed tees.
  • bob bob @ 9:28 PM
    Contact this user

    KCA

    I suspect what is going on is with the tank at A, fill pressure drops from the tank to the zone pumps. From the zone pumps back to A the pressure will increase . With three pumps in parallel the GPM of the pumps will add. You are pushing all that water through a 1" pipe causing the pumps to ride up their curves towards max head. This increase in pressure is seen by the boiler loop and is added to the 014. When you move the tank to B the head of the zone pumps is below fill pressure from B back to the pump inlets and reduces the pressure in the boiler loop. Try turning some of the zone pumps off and on with the tank at A and watch the pressure.
    bob
  • Big Ed Big Ed @ 8:08 AM
    Contact this user

    Hmmm

    I was thinking the same as I read down this post ... Breaking in to steam ? You would know by the hammering noise …Nothing was mentioned .

    I am thinking the change from the recommended piping to what was install which puts the circulators in series which adds up into the boiler . they are all pumping away from the tank . by relocating the tank on the heating return... The boiler circulator is pumping away as the heating circulator is pumping toward the tank... Hmmm.... Which takes them out of series

    I see the difference between the two diagrams . The heating zones are injecting in to the primary loop rather then the primary injecting into the secondary ..
    I have enough experience to know , that I dont know it all
    This post was edited by an admin on March 4, 2012 8:40 AM.
  • icesailor icesailor @ 8:37 AM
    Contact this user

    Over matched boilers:

    You don't always hear the sound of steam being made in a boiler like this like you might be used to hearing.
    If the rise in pressure is during high fire in the boiler, it's probably steam. You should be able to turn the fire down by modulating the flame to  low fire. Turn it down. Does it still rise in pressure and pop off? If it doesn't rise in pressure and pop off, there's part of the problem.
    I still saw that part of the flow issues are in the closely spaced tees. How far apart are they? Pictures? If the spacing isn't correct, it will act like Mark Ethertons notorious former BIL. He has his foolish friend with him. One will go around the lake in one direction. And his foolish pal will to but at a different speed. If they went at the same speed, one could ride the wake of the other for a better ride. Instead, they will have to cross each others wake. For a bumpy ride.
    They are using a 014 pump for the primary for the high flow through the boiler that is one inch through the boiler. Increased to 1 1/4" and reduced again to 1" through the closely spaced tees.
    Put your hand on the supply/primary pipe before it goes through the closely spaced tees. Run the boiler and if the boiler temperature rises to where you can't hold your hand on the primary side and you can (more or less) on the secondary side supply but the return of the secondary side isn't as hot, it's not mixing. If they all get hot together, the boiler is firing too high. Like many over-sized teapot boilers will do.
    The boiler is the engine. The heat emitting units are the radiation. If the engine is bigger than the available emitting system (radiators), the boiler will over heat.
    And I have said over and over, YOU didn't install and pipe it. HOW would have you done it differently. And that includes WOULD YOU HAVE USED THAT BOILER IN THAT APPLICATION???????
    Don't fall into the trap that the first installer made and don't use their logic on what they did. Use your own.
    Do you have enough installed radiation to cool 230,000 gross input into that boiler to cool it?  Turn it down to low-fire and see what happens. I told you, someone where I work has downfired a bunch of these boilers that were doing this. If you set it to low fire, and it stops, consider that.
    This post was edited by an admin on March 4, 2012 8:57 AM.
  • Big Ed Big Ed @ 9:02 AM
    Contact this user

    Just Curious ......

    Take a look at what was piped and what is recommended . The tees are reversed . What has changed ? Would be the question ...
    I have enough experience to know , that I dont know it all
  • Mark Eatherton Mark Eatherton @ 12:03 PM
    Contact this user

    Over thinking over pumping....

    Lets break it down to the basics.

    What influences water pressure. Pumps, and expansion.

    What is required in order to create thermal expansion? Heat.

    How much pressure can these circulators "generate" under ideal conditions? Is it enough to increase the pressure to the relief valves threshold? (I doubt it, even if they were in series)

    The expansion tank at B keeps the pressure stabile, but the tanks have been confirmed to be in good working order.

    If it were me, I'd eliminate fire from the equation first. If pressure remains stabile, then as others have said, you might be over fired, but something would have had to change DRASTICALLY to see that.

    Another possibility, the water ways of the aluminox boiler have become clogged, and the pump is creating significant back pressure, causing the relief valve to discharge. Possible but doubtful, because if it were clogged, the onboard controller would see th big delta and shut the burner down based on a no flow condition.

    And then, there is the real possibility that the T that the A expansion tank is tied into is rusted shut, hence no expansion acceptance ability.

    I have to give all of you credit for the thought you've given this, but I think we are over thinking the possibilities here. We are dealing with some fairly basic stuff here, and it hasn't always been a problem, so what changed?

    If worse comes to worse, leave the tank connected at the B point...

    Hang in there Ken, you will figure it out.

    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • bob bob @ 1:07 PM
    Contact this user

    Overthink

    Mark, I don't think we can over think this. Ironman came up with the way to correct the problem in the third post. I think it's worth trying to figure out WHY the tank doesn't work at A but does at B .
    bob
  • Big Ed Big Ed @ 3:37 PM
    Contact this user

    Hmmmm

    Question ? Is this a new instal ? Has the problem always been ?
    I have enough experience to know , that I dont know it all
  • KCA KCA @ 4:09 PM
    Contact this user

    Hard to say

    The gentleman has had two sidearms that have failed on him...  Both showed up by an increase in pressure in the heating system...  So now that they are fixed...  This has showed up..  System is about 6 months old..

       :-)  kCA
  • Big Ed Big Ed @ 4:54 PM
    Contact this user

    Two ?

    Two you say in six months ? Condemned for a pressure problem ... I guess we can assumed this has been a problem since it has been installed ... Question again ...has the pressure problems started since the start of the heating season ?
    I have enough experience to know , that I dont know it all
  • Big Ed Big Ed @ 5:01 PM
    Contact this user

    also

    where and how is the sidearm piped into the system in the first diagram ?
    I have enough experience to know , that I dont know it all
    This post was edited by an admin on March 4, 2012 5:03 PM.
  • KCA KCA @ 6:27 PM
    Contact this user

    The Sidearm

    is piped off the 1" supply manifold in the secondary...  On priority..

    Now it's a coil Weil McLain..  Before they were a tank in tank that someone installed..  Likely turned on the heating before the domestic was filled...

      :-)  KCA
  • Steve Whitbeck Steve Whitbeck @ 7:37 PM
    Contact this user

    tank

    It sounds to me like a bad tank - the system over pressures in just seconds after the burner starts - that means there isn't any room for expansion. I have had the diaphram get stuck to the top of the tank.
  • Paul48 Paul48 @ 8:57 PM
    Contact this user

    Six

    zones pumping from a 1' supply manifold, pumping at the PONPC?
  • KCA KCA @ 9:23 PM
    Contact this user

    ???

    It's pumping away...  Where do you see pumping at?  What am I missing...

      :-)  KCA
  • KCA KCA @ 9:16 PM
    Contact this user

    Yeah...

    I thought of that and changed tanks..  Same thing..

      :-)  KCA
  • Paul48 Paul48 @ 9:55 PM
    Contact this user

    In

    your original post approx. 2 weeks ago, you described this piping in detail, and I told you it was bass ackwards. In this posting,you drew the piping, and it is bass ackwards. You have hydraulic seperation between the primary and secondary loops, and you installed the expansion tank on the return of the secondary loop. "Pumping At"
  • KCA KCA @ 10:59 PM
    Contact this user

    Expansion tank "A"

    is on the supply...  I put a tank in the return Ex tank "B"and it repaired the problem..

    Is that what you mean? 
  • Harvey Ramer Harvey Ramer @ 10:53 PM
    Contact this user

    I bet if you ran the circs whithout firing the boiler the very same thing would happen.

    Imagine the secondary circs running without the primary circ turned on. We know they will create a pressure rise across the system that will drop back to close to 18lbs by the time it crosses the closely spaced tees. All is well. Now turn on the primary circ. It grabs the 18.5lbs, lifts it up and scoots it throught the boiler around the primary loop and (BANG...) hits the supply tee were the pressure may not be more then 18.5lbs. So the primary circ then creates a signifigant pressure drop on it's suction side. The supply tee cannot see this though because if it could it would transfer it right on up to the expansion tank and reverse the flow. The return tee wll see this pressure drop though. It will grab it and transfer it back across the system. As soon as it hits the seconday circs they will do what circs do,create a pressure dfferential. Only this time since there already is a pressure drop at their discharge they will merely multiply the pressure drop and send it on back to the expansion tank and the PRV. The expansion tank doesn't have enough capacity and the PRV makes up the difference. As the PRV is adding water we know the pressure has to be rising somewhere. The most logical place.. the discharge of the primary circ.

    At least, this is how I see it in minds eye.
  • KCA KCA @ 11:01 PM
    Contact this user

    Yeah but

    the prv is turned off...  and this happens..
  • icesailor icesailor @ 7:27 AM
    Contact this user

    Steam:

    Then the only source of the pressure can only be from steam expansion. You can't do that with pumps in a closed heating system.
  • Harvey Ramer Harvey Ramer @ 10:53 PM
    Contact this user

    I bet if you ran the circs whithout firing the boiler the very same thing would happen.

    Imagine the secondary circs running without the primary circ turned on. We know they will create a pressure rise across the system that will drop back to close to 18lbs by the time it crosses the closely spaced tees. All is well. Now turn on the primary circ. It grabs the 18.5lbs, lifts it up and scoots it throught the boiler around the primary loop and (BANG...) hits the supply tee were the pressure may not be more then 18.5lbs. So the primary circ then creates a signifigant pressure drop on it's suction side. The supply tee cannot see this though because if it could it would transfer it right on up to the expansion tank and reverse the flow. The return tee wll see this pressure drop though. It will grab it and transfer it back across the system. As soon as it hits the seconday circs they will do what circs do,create a pressure dfferential. Only this time since there already is a pressure drop at their discharge they will merely multiply the pressure drop and send it on back to the expansion tank and the PRV. The expansion tank doesn't have enough capacity and the PRV makes up the difference. As the PRV is adding water we know the pressure has to be rising somewhere. The most logical place.. the discharge of the primary circ.

    At least, this is how I see it in minds eye.
    This post was edited by an admin on March 4, 2012 10:55 PM.
  • Paul48 Paul48 @ 11:07 PM
    Contact this user

    I

    Don't know whether it is possible, but it wouldn't shock me if there was a thump from the flow control closing just before the valve discharged.
  • icesailor icesailor @ 7:22 AM
    Contact this user

    Flow Control:

    If that is the case, manually open the flow control valve and the problem should stop.
    I installed a Munchkin once. I had my son pipe it. I gave him explicit instructions with a diagram on how to pipe it. He piped it as he understood the drawings. When I fired it off, because the piping was screwed up, the primary pump didn't come on for a heat call. It would run for a few minutes and a very few minutes, then the pressure would rise QUICKLY and the relief would blow. It was flashing in the boiler from lack of flow. There's a pressure switch but no flow switch.
    I still say, there's not proper flow through the boiler. If the supply loop gets hot quickly on the supply and return but not getting hot as fast into the secondary loop, there is a problem with the hydraulic separation
    Pumps piped in parallel can not raise pressure any higher than the highest rated pump in the system/circuit. Pumps piped in series can. That's how multistage pumps work. Each pump ads multiplication to the next pump by boosting the water from the first pump. But it can't have an outlet as it goes to the next pump. That's why Hydraulic Separation works.
    Turn the boiler down to make it run on the lowest fire possible. If it stops, the flow is either too slow, the boiler is over fired for the load or a combination of both.
    Whether you all want to believe it or not, someone I know where I work and does gas service work has gotten a lot of these complaints. He "solves" them by down rating or down-firing the boilers. Then, the problem goes away. He is absolutely convinced (right or wrong) that these teapot boilers are way over sized for their applications. I tend to agree.
    And I ask again and say again. You didn't install or design this problem. Have you done a heat loss on the building? Is the boiler (230,000 BTU's Gross) properly sized for the application? When only one zone is calling, is "Low Fire" low enough to keep the boiler from overheating?
    FWIW (nothing)
  • furnacefigher15 furnacefigher15 @ 11:24 PM
    Contact this user

    Mark is right.

    This is simpler then we are making it.

    There is probably something wrong with the spirovent that is blocking the flow of water into the exp tank at point A.

    This system with it's undersized piping is probably experiencing higher then normal water velocity, and that velocity is polishing the cast aluminum in the boiler. Those particles have made there way into the spirovent and are mucking up the works.

    The spirovent makes for a good strainer too.
  • KCA KCA @ 11:46 PM
    Contact this user

    Interesting that you said that

    The owner has $10 on it...

      Lol..  It might be...  I'm going to pull it apart tomorrow

    :-) KCA
  • icesailor icesailor @ 7:25 AM
    Contact this user

    Pressures:

    Unscrew the #1 Extrol, add a 1/2" Bl Tee and bush it to put a pressure gauge. See if the pressure fluctuates at the Extrol when the "event" happens. Put one in place of the boiler darins around the system. You guys are just guessing. You need hard facts.
    GAUGE IT!!!
  • Paul48 Paul48 @ 11:49 AM
    Contact this user

    I

    agree, and in all these posts there is a procedure to determine the cause of your problem. Get a pen and paper. Start at the top of the post, and add all the tests you have not done.Start with the simplest, which is most likely ices. Is the tank at position "A" seeing pressure change?
  • Big Ed Big Ed @ 1:39 PM
    Contact this user

    Agree

    Sure we are only guessing from behind a key board . First it's piped wrong from the start ... Seems it always been a problem ... I would also assume the boiler is over sized finding 99% are out there are , that makes sense too .... Most likely a combo of both ...

    If it were me I would repipe the boiler to factory spec first ... That is the first obvious problem which should be addressed , Any court of law would agree ... And yes drop down the heat output to its load . That is the beauty of these boilers ... After that blockage should be addressed if problem still exists

    Seems all the obvious , Feed valves , heat exchangers , domestic bypass , tank and tank pressure has been addressed ...

    Moving the tank from point A to B. ... What changes ? We all know pressures with circulators will change ... But why so dramatic to pop the safety ? The improper piping has to be an issue and that boiler also calls for that 0012 then add a high output boiler .

    Being a hands on guy myself. I need to touch and look to find the problem, that and the learning knowlage of how it should work . Then test to cut down the odds :) I am sure we are all doing the same ...
    I have enough experience to know , that I dont know it all
  • hot rod hot rod @ 12:00 PM
    Contact this user

    the relief valve

    has been blowing off since it was installed, possibly. If so the HX could be partially plugged fropm all that fresh fill water. How hard is the fill water?

    I'd agree that the connection to the tank from the purger is obstructed.

    hr
  • Paul48 Paul48 @ 12:45 PM
    Contact this user

    It's

    worth eliminating it. Remember, he said it does it at 120 or 180 degress, it doesn't matter.Which tends to lead me away from normal thermal expansion in a properly operating system.The process of elimination will get to the root of the problem.
  • KCA KCA @ 8:00 PM
    Contact this user

    OK... Here's what it was

    I pulled the top off the spirovent and..  Well take a look at the pics..

    Apparently, Spirotherm installs these in the spirovents but it looks like this one got installed upside-down...

    This would have been the last thing I would have expected...  But then there is a lesson in that for ya..

    By the way...  With all zones on the pressure buildup is about 2.5psi...

    Thanks everyone............

    :-)  KCA
    This post was edited by an admin on March 5, 2012 8:03 PM.
  • Mark Eatherton Mark Eatherton @ 8:59 PM
    Contact this user

    I told you you'd find it....

    Good job.

    Hooda thunk....

    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • Steve Whitbeck Steve Whitbeck @ 10:09 PM
    Contact this user

    Good Job

    So the water wasn't getting into the tank after all. When you are pulling your hair out it is usually something stupid. ( in this case the manufacturer)
  • Big Ed Big Ed @ 6:14 AM
    Contact this user

    Funny

    The feed valve was connected to the same connection. There was no problems feeding the system ? You should have caught that
    I have enough experience to know , that I dont know it all
    This post was edited by an admin on March 6, 2012 6:16 AM.
  • Steve Whitbeck Steve Whitbeck @ 8:23 PM
    Contact this user

    Big ED

    The feeder pushes water in - System water expansion pushes water out and into the tank.  The plastic insert was acting like a check valve blocking the bottom outlet to the exp. tank.
  • Gerry Alder Gerry Alder @ 9:52 PM
    Contact this user

    I throw out the plug

    The purpose of the plug inside the spirovent strainer is to slow the flow for when someone might do a fast fill like at startup it helps keep the vent from spitting water . Then later you run into problems like this one.
    ENJOY YOUR HEAT AND HOT WATER.
  •  