  • plumber_ted plumber_ted @ 7:54 PM
    Contact this user

    Beckett pump coupling

    I was recently working on an older Beckett oil burner.  I had pulled the motor and blower wheel out to clean them.  The owner was there watching as I was working and had told me that the last tech had removed something from "in there" last time.  Upon further inspection I noticed that the other company had removed the pump coupling with the "inlet air shut off".  I believe that beckett had this type of coupling installed for a reason.  Does anyone know why? and also would anyone have a part# for this so I can get a replacement.
    Thanks in advance
  • icesailor icesailor @ 8:54 PM
    Contact this user

    Beckett Pump:

    The previous tech did a fine thing by removing that "thing". Do yourself a favor and don't try to replace it. It can and will be a problem. And is why the previous Tech removed it. It is supposed to be an automatic air shutter that stops air flow through the burner when it isn't running, They often stuck partially open.
    Don't replace it.
  • LIBob51 LIBob51 @ 1:10 AM
    Contact this user

    those things

    Do nothing but cause noise complaints. Removing it makes it much easier to clean the inside of the air gate too. Sure the burner fan may need cleaning on each visit, but it should be done regardless
  • David Sutton David Sutton @ 1:25 PM
    Contact this user

    Air inlet damper

    i belive those were recalled about 15 to 20 yrs ago, They would stick shut and plugged the boiler up with wet sloopy soot, never leave one in.
  •  