Compressor shut down
I have a unit thats shutting down , on high anbient conditions . Runs well , when we get to 100 ° F it trip the breaker.
Breaker
What is "circuit breaker ampacity "of the unit and what breaker is in the panel and what amps is the unit pulling?
Need some info
Pressures and temps at 100* if possible. Condition of contactor and electrical in general. Amp draw on compressor and cond. fan. All you are saying is it's broke at 100*, please fill in the blanks.
Mike T.
Need more info.....
As Empire said, need more info. Could be so many things. Amp draws and superheat/subcooling. Also capacitor weak? Outdoor fan motor going out on internal overload? Does the unit have a high pressure switch? Electrical connections tight? Proper wire size? May need hard start kit.