  • Steve1000r Steve1000r @ 7:45 PM
    Contact this user

    Rinnai q130 boiler

    Got a q130 boiler that won't fire. Boiler tech told me it may need an outside reset. My understanding is that these units fire once it senses flow. I have a 3 zone hydronic system with 3 brand new taco IFC circulators with a 4 zone taco relay. WHAT the hell could be wrong? Any1 got advice your help is appreciated
  • nicholas bonham-carter nicholas bonham-carter @ 10:09 PM
    Contact this user

    Proper selection

    Is this a domestic water heater being used for hot water heating?
    If it is, keep it feeding your hot water needs, and get a boiler.--NBC
  • HDE HDE @ 11:31 PM
    Contact this user

    Not a tankless

    It's an Atag boiler imported from UK and labeled Rinnai.

    Sorry too much to diagnose to give you an easy answer, no magic button to push on this one.
    This post was edited by an admin on November 3, 2012 11:39 PM.
  • Jack Jack @ 9:36 AM
    Contact this user

    Pre-purge

    Does the unit run through the pre-purge cycle? It is 17 min on start-up!
  • Steve1000r Steve1000r @ 5:39 PM
    Contact this user

    Solved

    Problem solved! You gotta run t stat wire from "xx" on the relay to 22 and 23 on the boiler. Unit fired right up!
  • Steve1000r Steve1000r @ 5:39 PM
    Contact this user

    Solved

    Problem solved! You gotta run t stat wire from "xx" on the relay to 22 and 23 on the boiler. Unit fired right up!
  • HDE HDE @ 7:13 PM
    Contact this user

    You never said it was a new install

    More than once an installer expected products from different manufacturers to magically wirelessly talk to each other.

    If you didn't know they can't it must be a DIY install, hope other things go as well for you.
  •  