Need Assistance with TACO RMB
Hi,
I was going to use the TACO RMB as a setpoint control but outdoor design needs to be turned off. I couldn't find a way to do this from the directions. Could someone please help me with this?
Thank you
Disconnect outdoor sensor?
I seem to recall that would do it...
Setpoint operation of the RMB
When in the adjust menu, you need to program the OUT DSGN (outdoor design) to OFF.
Also program the Delta T to OFF
Then program your MIX TARG (mix target temp) to your desired temp. The Range is 60-200 and the default is 140.
Enjoy
Dave H