Honeywell pressure switch
Has anyone noticed a lot of these Honeywell pressure switches failing on Luxaire/York furnaces? Its the one that measures pressure difference between the exaust and intake on direct vent systems.
The switch I'm looking at is a model 9371-DO-HS-0010 and it has failed already in less than a year after replacing the first time. Now, giving it a bump will get it working again for a while until it sticks again (sounds real safe, right?).Boiler pictures.
https://picasaweb.google.com/thetube0a3/Boiler?authkey=Gv1sRgCImUxIqv9436MQ#
Weil-McLain EG-45 connected to 392sqft of radiation via two 2" risers into a 3" drop header and 2" equalizer. Using Rectorseal Steamaster water treatment to greatly reduce corrosion in the boiler. -
Is it...
A positive or negative pressure switch? (monitors inducer or HX)
I've found on reoccurring issues the number of elbows or length or vent was right at max.Working on steam and hot-water systems isn't rocket science....it's actually much harder. -
negative
It says -1.00WC on it so I'm assuming thats a negative pressure switch.
I know the exhaust and intake lines are almost identical, one has an extra 45 to offset it some. Also the lines are 1 elbow short of the recommended maximum except the intake has that extra 45 which moves it even closer to the max I guess.
Would modifying the lines and removing any elbows possible give the switch less of a chance of failing?Boiler pictures.
https://picasaweb.google.com/thetube0a3/Boiler?authkey=Gv1sRgCImUxIqv9436MQ#
Weil-McLain EG-45 connected to 392sqft of radiation via two 2" risers into a 3" drop header and 2" equalizer. Using Rectorseal Steamaster water treatment to greatly reduce corrosion in the boiler.This post was edited by an admin on December 9, 2012 11:00 PM. -
Yes
I would say not being 1 45* elow from max would surely help. Fieldpiece makes a sweet new pressure switch testing instrument but I don't have one yet because a failed pressure switch is uncommon. It's more likely your altitude or fittings/pipe size being near max. You can increase pipe size if fewer fittings is not possible. Use your analyzer to test negative pressure at the inducer.Working on steam and hot-water systems isn't rocket science....it's actually much harder. -
altitude
Altitude is around 2000 feet.
After looking at it we decided we can eliminate 4 90 deg ells and replace them with 3 45s.
Thanks for your help, I appreciate it.Boiler pictures.
https://picasaweb.google.com/thetube0a3/Boiler?authkey=Gv1sRgCImUxIqv9436MQ#
Weil-McLain EG-45 connected to 392sqft of radiation via two 2" risers into a 3" drop header and 2" equalizer. Using Rectorseal Steamaster water treatment to greatly reduce corrosion in the boiler.This post was edited by an admin on December 10, 2012 9:56 AM.