trap
Looks like an old school F&T trap with an external T part, hard to say, describe where the piping is coming from and going to
RJ
I think
that's a "float trap/air eliminator" as described in chapter 15 of Lost Art. It is the only place where air is vented from the system.
Is this device on the dry return near the boiler?
Steam trap
Yes the trap is located on the return
This post has been deleted!
I agree.
It's a central air eliminator. The float keeps the boiler water from flowing out the vent hole. It's not a steam trap.
Looking at it
Sideways I believe and my first thought was also some kind of vent.
trap
Take a temp. reading from inlet to outlet, if the temp is the same this would indicate a problem with the trap, it can be replaced with a Hoffman F&T trap. there would be extensive repiping
RJ
no trap
Thanks Dan for the clarifiiation looked like an old trap but the piping did not seem right
RJ
I'm glad you asked.
A trap in that spot would have hurt.
Steam trap
Thank you for the info, now for 64 thousand dollar question, what can replace it.
Is it broken?
If so, a high-capacity main vent. But if it still vents I'd leave it.