pressuretrol on burnham V9a
hello my Burnham v9a has two pressuretrol boxes on it, would like to know where setttings should be. pressuretrol on left has diff @ 2.5psi and main @ 5psi. right pressuretrol only has main which is set @ 7psi
Try...
changing the left one to a differential of 1 psi and a cutin of 0.5 psi if it is additive, or a cutout of 1.5 psi if it is subtractive. Leave the other one at 7.
Jamie
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch