converted oil to gas
i recently converted 3 boilers from oiled fired to gas fired using the ez carlins gas bruners on 2 of the boilers( both well mcclains) and a G3B burner on a utica boiler Starfire 3 model. The 2 ez carlins are running fine but i have received a question regarding gas usage on the utica. While the 2 ez carlins installs showed a 2/3rds increase in gas useage, the utica gas usage has tripled if not 4X creating a massive gas bill. Any thoughts on why or if there is some solutions. All boilers are steam boilers and were all cleaned and soot vacced. -
Burners
Did you install a draft control? Did you match the existing BTUH input? What were your combustion numbers?- Joe Starosielec
Metuchen, NJ -
yes
yeah has a draft control....combustions numbers are 9.7 co2........3.6 o2....stack temp at 574f with 27% EA...and i matched existing btu from boiler to the burner and drilled the orifice accordlly -
i didn't
even know they still made the g3b. i havn't needed parts for any ever so... -
I wouldn't have used the G3B on that Starfire-3
it needs more static air pressure than the G3B can produce. That's why the original Beckett burner on these boilers is an AFG rather than an AF- the AF doesn't produce the static air pressure that the AFG can.
Swap the G3B for an EZ-Gas, with the proper air tube for that boiler, and it'll run much better."Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere. -
thx
ok lemme give that a try