  • tpowls84 tpowls84 @ 10:14 PM
    Contact this user

    Advice on heating unit

    Separating the utilities on a 2 family home. Currently have a steam boiler working both floor with the thermostat on the first floor. I want to run a loop of baseboard on the second floor. And separate the hot water. It's a small area. After a heat loss calculation, I'm getting a heat loss of about 20k buts. I'm interested in a combi boiler but can't seem to find one to fit such a low btu output. Any advice would be appreicated.
  • Steve Whitbeck Steve Whitbeck @ 10:24 PM
    Contact this user

    seperate systems

    I would not recommend any combi water heaters. They will be more trouble and cost more in maintenance.
    I would go with a small boiler and separate water heater.
    Water heaters are cheap to replace and being a commercial job the indirect would not have a good warranty. Since You will not be paying the gas bill I would go with a small cast iron boiler and a standard water heater. LOW initial cost and LOW cost of maintenance.
  • This post has been deleted!

  • This post has been deleted!

  • tpowls84 tpowls84 @ 10:28 PM
    Contact this user

    Limited space

    I can barely fit a water heater in the utility room. That's the reason I considered a combi.
  • JStar JStar @ 6:04 AM
    Contact this user

    Boiler

    http://www.cadetboiler.com/

    The lowest Cadet boiler is 40,000 input, or 37,000 output. For such a low heating load, you would not have enough power to supply any reasonable domestic water load, unless you installed a buffer/indirect tank with a bigger boiler, which is not the greatest for fuel efficiency. Better off going with separate heat and dhw units.
    - Joe Starosielec
    http://thatcherhvac
    http://facebook.com/thatcherhvac



    Guaranteed performance. Guaranteed energy savings.


    Serving all of NJ, NYC, Southern NY State, and eastern PA.

    Consultation anywhere.

    (Formerly "ecuacool")
  • SWEI SWEI @ 11:03 AM
    Contact this user

    20k space heating load

    Would lead to a direct-vent gas like the RInnai Energy Saver, since there's almost nothing else that's really sized right.  I'd probably be looking at a mini-split heat pump or perhaps even an electric resistance boiler with ODR control like an  Electro or a Thermolec.  Pretty sure the Slant/Fin doesn't come that small.
    This post was edited by an admin on March 27, 2013 11:04 AM.
  • Steve Whitbeck Steve Whitbeck @ 8:31 PM
    Contact this user

    cieling height

    How much ceiling height do you have?
    You could always put a 40 gallon superstor on the floor.
    And build a stand to put the boiler above it.
  •  