  • kcopp kcopp @ 8:27 AM
    Contact this user

    Lp gas pressure "conversion"

    I have a customer who has an existing direct vent water heater that is LP gas fired. It is on its last legs and leaking. He would like to replace it w/ a tankless fired unit. Problem is that the copper gas line runs over a finished space and is undersized. Is it possible to convert that to a 2# set up and then put a step down regulator in? What has to happen at the tank? New regulator or just an adjustment?
    This post was edited by an admin on April 11, 2013 8:30 AM.
  • Aaron_in_Maine Aaron_in_Maine @ 8:47 AM
    Contact this user

    Yes

    Yes you can as long as nothing else is on that line. You will need a new regulator at the tank and a maxitrol for your new tankless. If there are other appliances on that line then they will need maxitrols as well.
  • TonyS TonyS @ 8:54 AM
    Contact this user

    It depends

    If you have two step regulation, A 10# at the tank and a 11 inch wc at the house, then you will only need to change the one at the house and add another inside.
    If you have a two stage single regulator you will need to replace the one on the tank .
    Download the serviceman's manual and the products catalog. It will show you everything. http://www.regoproducts.com/LPG/Products.html
    Remember to check and see if the tank will be large enough to supply the gas without freezing up. The tables are in the manual.
  •  