  • smokes smokes @ 9:16 PM
    Contact this user

    Adding a hydronic zone to a steam system

    Hey - I have a steam system running off a Burnham about 10 years old, with a hydronic baseboard loop in the basement with its own simple honywell 120v thermostat and circulator pump. The thermostat basically controls the circulator pump not the boiler.
    My question is can i set up the system so the hot water loop will call for heat and fire up the boiler without burning up the radiators upstairs?
    if not, would it be practical to add a tankless water heater to run the basement heat seperately? Can that set up work?
  • Jamie Hall Jamie Hall @ 10:20 PM
    Contact this user

    It's late at night so I'll be quick

    and others will probably expand on my comments...

    Yes, you can set up an aquastat to run the boiler when the hydronic zone calls for heat and the boiler water isn't hot enough.  No, there is no simple way to keep the boiler from then heating the radiators upstairs.  It might, it might not, depending on how you have the controls wired and a few other factors -- and it wouldn't be very consistent.  Tankless water heaters are not, in general, recommended for use on hydronic heat systems...
    Jamie

    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.

    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • Steamhead Steamhead @ 10:36 PM
    Contact this user

    Actually

    it can be done, and will work well. The key is wiring the aquastat so it won't let the boiler make steam when only the HW loop is calling. 
    "Reducing our country's energy consumption, one system at a time"

    Steam, Vapor & Hot-Water Heating Specialists

    Oil & Gas Burner Service

    Baltimore, MD (USA) and consulting anywhere.
  • smokes smokes @ 11:49 AM
    Contact this user

    Great!

    Thank you, gentlemen and scholars! Its amazing how you can get great answers on this website! I'll check with my plumbing supply and let you know how it works out.
  • JeffM JeffM @ 2:45 PM
    Contact this user

    commonly done

    Your aquastat would be just like the ones used to control tankless coils in a boiler - they keep the boiler hot, but shut it off before it boils so you're not sending steam to the radiators just by running a hot water faucet. 
  •  