    Another triangle tube install question

    Before I contact my installer, I am getting ghost flow on my primary return pipes from my heating zones when the indirect Is getting heat. Should there be a near boiler check valve installed even though I have check valves on all my zones? Also, I had a system bypass on my old heating system, should the valve be open or closed?
    Thanks in advance
  • Zman Zman @ 8:36 AM
    Contact this user

    110?

    The tt 110. with the factory installed circ does not have a check valve in the circ. This will cause major ghost flow to the secondary. Some of that is going out your returns. If this is the case, the easiest thing to do is to snap a grunfos check valve into the boiler circ.
    Carl
  • wrxz24 wrxz24 @ 12:36 PM
    Contact this user

    as opposed to

    to put one on the return line from the heating zones.  I think I saw something in the manual for best practice to put a near boiler check valve in.  But the check valve in the circulator will do the trick?  is there a part # for this? Thanks
  • Zman Zman @ 8:53 AM
    Contact this user

    Check Valve

    I asked the triangle tube guys why they don't just use a circ with a check valve, They said they were not as durable. I have done it quite a few times and have never had a problem. I don't know where to buy them.Since most grudnfos circs that size come with them and they often are not needed, I usually has a few laying around. You might try calling grundfos or your contractor, It is not a big deal to sweat one in, it is just much easier to unbolt the circ and snap it in.
    Carl
  • wrxz24 wrxz24 @ 10:16 AM
    Contact this user

    Thanks, Another question

    Would opening up the system bypass help? It is closed down currently. Thanks
  •  