    Do all LWC's Need

    moving water to keep them operating without false shut downs?
  • Rich Rich @ 2:24 PM
    Contact this user

    No

    is there one that needs moving water ?
    You didn't get what you didn't pay for and it will never be what you thought it would
  • ced48 ced48 @ 2:31 PM
    Contact this user

    I Was Warned

    against putting one in a dead end, even with a vent-bad advise?
  • SWEI SWEI @ 3:52 PM
    Contact this user

    It's about system temperature

    so a dead end is not going to read that very well, unless the LWCO has a probe long enough to get back into an active pipe (installed in the end of a tee, typically.)
  • Zman Zman @ 6:46 PM
    Contact this user

    The dead end..

    Could also plug up with sediment.
  • rick in Alaska rick in Alaska @ 11:26 PM
    Contact this user

    dead end

    The dead end can also have an air pocket that can be hard to get out, which will make the control shut the system down since it is not covered with water.
    My 2 cents anyway.