    I haven't done one yet and I have always been worried about snow blocking a boiler vent through the roof, but I have never heard about the problem. has anyone experienced a problem? I live in northern Massachusetts.

    Thanks, Bob Gagnon
  • Steve Whitbeck Steve Whitbeck @ 11:42 PM
    Contact this user

    snow

    Snow can block the intake so mount it up as high as it can go. Also I extend the center pipe up another 12 to 18 inches to stop reversion on very cold days.
    On very cold days the exhaust gasses are not hot enough to rise and can fall down and into the intake.
  • Steve,

    You put and extension pipe into the middle of the concentric vent?
    Thanks, Bob Gagnon
  • radmix radmix @ 7:35 AM
    Contact this user

    Yes

    I do it all the time with no problems. I live in upstate N.Y.
  • pipe4zen pipe4zen @ 2:50 PM
    Contact this user

    extend

    Code requires a minimum of 12" above roof measured from bottom vent cap at air intake.
    You can extend, do not use couplings, only full length pipe of the same diameter. Maximum that can be extended is 60" total. Dont forget to add new length to equivalent totals for exhaust run from boiler to determine if you are under 100' total length.